Re: Help with Planning & Building of my Recording Studio
Alright, I've got yet again another question relating to floor isolation. I'm still waiting to hear back from my architect/engineer with the right numbers so in the meantime as stated in my previous post, I'm trying to figure out other options. The implicated troubles and associates costs in attempting to float a concrete floor might be too much. I guess this is why they call this the "Planing Stage" haha.
Anyways, I've been looking at other options for isolating my floor and I thinking that my worst case scenario is I would be going with a "damped deck" style floor. I believe this could at least give me some extra isolation and would really help with flanking noise. Even with this type of floor the weight will be pretty high. I've estimated that this entire floor would be approx. 5000lbs. This is just the floor alone, I still need to calculate the weight of the walls, window, doors.
So looking at the materials required for the suggested damped deck. I know it's asking for OC 703 semi rigid insulation. Unfortunately this type of insulation isn't that available around here and I'm looking at this following product. I was wondering if based on the specs this would be a suitable replacement for the OC 703.
http://www.roxul.com/products/comfortboard-110/
Anyways, I've been looking at other options for isolating my floor and I thinking that my worst case scenario is I would be going with a "damped deck" style floor. I believe this could at least give me some extra isolation and would really help with flanking noise. Even with this type of floor the weight will be pretty high. I've estimated that this entire floor would be approx. 5000lbs. This is just the floor alone, I still need to calculate the weight of the walls, window, doors.
So looking at the materials required for the suggested damped deck. I know it's asking for OC 703 semi rigid insulation. Unfortunately this type of insulation isn't that available around here and I'm looking at this following product. I was wondering if based on the specs this would be a suitable replacement for the OC 703.
http://www.roxul.com/products/comfortboard-110/
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
I also wanted to mention that I've just donated some funds to this site to show my appreciation for all of the help around here. Cheers!
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
Alright, so it's obvious I knew this was coming but it's been confirmed that my current structure/floor cannot support a floating concrete slab. That being said, I know it's not impossible as I do have options to install a steel support beam with a few posts and that would get me what I need to go the concrete route, BUT....I've decided I'm not going to go down that path after all because there are other things I'd like to spend my money on with this studio build. I'll just accept the situation and move forward.
I went back to my architect and asked if I could at least go with a damped deck style floor and will wait until he gets back to me. I don't think it'll be a problem but will make sure. The composition I understand is 2 x layers of 3/4" MDF with GG...on top of OC 703 or equivalent.
Other than this Glenn recommended damped deck option...are there any other known decent options that I could compare with?
I went back to my architect and asked if I could at least go with a damped deck style floor and will wait until he gets back to me. I don't think it'll be a problem but will make sure. The composition I understand is 2 x layers of 3/4" MDF with GG...on top of OC 703 or equivalent.
Other than this Glenn recommended damped deck option...are there any other known decent options that I could compare with?
-
Soundman2020
- Site Admin
- Posts: 11938
- Joined: Thu Aug 21, 2008 10:17 am
- Location: Santiago, Chile
- Contact:
Re: Help with Planning & Building of my Recording Studio
That's unfortunate, but not unexpected.it's been confirmed that my current structure/floor cannot support a floating concrete slab.
Expensive, but workable. That's the real solution IF you need very high isolation, which you seem to do.I do have options to install a steel support beam with a few posts and that would get me what I need to go the concrete route
I would suggest one layer of plywood and one of MDF, with GG if you wish.The composition I understand is 2 x layers of 3/4" MDF with GG...on top of OC 703 or equivalent.
As long as you understand that this is not going to be as good as a proper floated floor, and that there will be some transmission of sound in both directions, then this is a possible alternative.
- Stuart -
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
Yeah that's for sure but I'm okay with it.That's unfortunate, but not unexpected.
The main reason why I'm not proceeding with a floated slab is simply because I feel as it would be a lot of money invested for too small of an area. That being said, I'm planning to build a big garage in the near future behind my property. I've decided that when that time comes (5-10 years), I will likely just make the building bigger and incorporate/move my studio there. With all of this new knowledge I will just build it perfect from the start with individually floated slab. Then I can set my isolation goals much higher then but for now, I will take what I can get and manage the loudness. I still believe I can build something half-decent isolation wise and great sounding.Expensive, but workable. That's the real solution IF you need very high isolation, which you seem to do.
Would laying down an additional 3/4" MDF directly on my sub-floor with GG, under the deck help a little bit?I would suggest one layer of plywood and one of MDF, with GG if you wish.
Yes, I do understand. From this point on I'm just going to do the best I can to get the max out of my current floor and live with that. Again, I'm not always going to be playing at 120db level so I think isolation of low frequencies can be managed.As long as you understand that this is not going to be as good as a proper floated floor, and that there will be some transmission of sound in both directions, then this is a possible alternative.
Alright back to having questions.....
1) Going with the damped deck idea, would anyone have any other suggestions with respects to isolating my shitty
2) I'm wondering if I should i even bother with trying to build a room within a room now since I know I can't expect high levels of isolation. I should still build double studded partition walls right? I just need to confirm that my original idea for wall and ceiling composition is valid and not a total waste of money haha.
I know I've been saying this for a while but I'm AM almost done with my sketchup plans. I may have gotten overboard with the drawing hahaha. it's fun!!
Again, thanks for your patience and time!
Cheers,
Francis
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
Hey all, just wanted to write a quick little update on my planning. Things have been really really slow with this project but the good part is that at least I'm moving forward a little bit each time I post and plus I figure it's a good thing to document the progress on here. Most of my focus and time has been aimed at planning. I've stopped building things and am reading and researching more.
I've read A LOT of threads and I'd say 95% of the people here who have the same structural properties as I do have either given up on their projects or just never bothered to come back to share progress and/or final results. I'm committed to doing things the best I can within the limits/boundaries I've got.
I finally got the "official" numbers back from the engineer and my current constructed "timber" floor is able support 33psf dead load. Except for the floating concrete slab, he gave me the green light to build with the composition I had originally planned.
Floors - Dampened Deck (1x 3/4" MDF, 1x 3/4 OSB", 2" Rigid Isolation)
Walls - Double Stud Walls (2x 5/8" Type-X Drywall, Green Glue)
Ceilings - Hat Channel, Sound Clips, 2 x 5/8" Type-X Drywall, Green Glue
Now that I have that information confirmed, I'm going work on a floor plan and layout and try my best to come up with a decent draft. That being said I'm trying to find examples of similar builds but no luck. The thing I struggle with the most right now is trying to address the fact that my room is a big triangle and I have yet seen any designs or floor plans for a large "attic type" home studio. I'd like to try and calculate/evaluate modes and figure out the best ratios but how can this be done with a room like mine versus a rectangular room?
I'm also trying to determine if I should cancel out the Vocal/Amp Booth and make the CR bigger and just have a Live Room and Control Room. Any ideas or suggestions would be greatly appreciated.
I've read A LOT of threads and I'd say 95% of the people here who have the same structural properties as I do have either given up on their projects or just never bothered to come back to share progress and/or final results. I'm committed to doing things the best I can within the limits/boundaries I've got.
I finally got the "official" numbers back from the engineer and my current constructed "timber" floor is able support 33psf dead load. Except for the floating concrete slab, he gave me the green light to build with the composition I had originally planned.
Floors - Dampened Deck (1x 3/4" MDF, 1x 3/4 OSB", 2" Rigid Isolation)
Walls - Double Stud Walls (2x 5/8" Type-X Drywall, Green Glue)
Ceilings - Hat Channel, Sound Clips, 2 x 5/8" Type-X Drywall, Green Glue
Now that I have that information confirmed, I'm going work on a floor plan and layout and try my best to come up with a decent draft. That being said I'm trying to find examples of similar builds but no luck. The thing I struggle with the most right now is trying to address the fact that my room is a big triangle and I have yet seen any designs or floor plans for a large "attic type" home studio. I'd like to try and calculate/evaluate modes and figure out the best ratios but how can this be done with a room like mine versus a rectangular room?
I'm also trying to determine if I should cancel out the Vocal/Amp Booth and make the CR bigger and just have a Live Room and Control Room. Any ideas or suggestions would be greatly appreciated.
Last edited by Studio45 on Thu Nov 30, 2017 2:42 am, edited 1 time in total.
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
Alrighty! I've finally gotten around to updating my construction plans for the studio. I know it's going to need some adjustments but this will give everyone a better view of what I'm trying to do. I'm going to delete the older ones as they're of no use anymore.
As it stands the plans shows the rooms as follows:
Live Room is 14' x 20'
Control Room is 12' x 8.8'
Iso/Vocal Booth is 6' x 8.8'
The .skp file was too big so I'm sharing a link to where the file can be downloaded.
https://drive.google.com/open?id=1jsJ93 ... mVH5HJj0q1
Let me know if you're having any issues.
As you'll see its not a completed plan by any means. After reading more and more I've had to make a lot of changes to it but I think it's getting better each time.
Right now I'm dealing with the following issues:
1) Having a hard time trying to figure out how to connect/close off the live room with the entrance of the studio. There's a little storage area to the right of the door that I want to use but doesn't need to be accessible from inside the live room. That's what I'm working on right now.
2) I'm not sure what to do with my ceilings. I originally was planing on using the existing ceiling and install sounds clips and hat channel with 2 x 5/8" drywall but at this point I'm starting to like the idea of building individual ceilings for each room. The biggest drawback I feel is the extra space I'm going to end up taking doing that but I assume the isolation would be much better.
3) Debating if I should shrink or cancel out the Iso/VocalAmp Booth to make the CR bigger. Worst case I'd be happy and fine with having just a Live Room and Control Room.
Not shown is the the HVAC closet located on the left side of the door. This area is closed off but is accessible from outside the studio within another storage area
Any feedback is appreciated!!
In the meantime I'm going to try and add more details such as the HVAC closet and storage area as well as try and finish the area where the entrance/storage area/live room meet up.
Cheers!
Francis,
As it stands the plans shows the rooms as follows:
Live Room is 14' x 20'
Control Room is 12' x 8.8'
Iso/Vocal Booth is 6' x 8.8'
The .skp file was too big so I'm sharing a link to where the file can be downloaded.
https://drive.google.com/open?id=1jsJ93 ... mVH5HJj0q1
Let me know if you're having any issues.
As you'll see its not a completed plan by any means. After reading more and more I've had to make a lot of changes to it but I think it's getting better each time.
Right now I'm dealing with the following issues:
1) Having a hard time trying to figure out how to connect/close off the live room with the entrance of the studio. There's a little storage area to the right of the door that I want to use but doesn't need to be accessible from inside the live room. That's what I'm working on right now.
2) I'm not sure what to do with my ceilings. I originally was planing on using the existing ceiling and install sounds clips and hat channel with 2 x 5/8" drywall but at this point I'm starting to like the idea of building individual ceilings for each room. The biggest drawback I feel is the extra space I'm going to end up taking doing that but I assume the isolation would be much better.
3) Debating if I should shrink or cancel out the Iso/VocalAmp Booth to make the CR bigger. Worst case I'd be happy and fine with having just a Live Room and Control Room.
Not shown is the the HVAC closet located on the left side of the door. This area is closed off but is accessible from outside the studio within another storage area
Any feedback is appreciated!!
In the meantime I'm going to try and add more details such as the HVAC closet and storage area as well as try and finish the area where the entrance/storage area/live room meet up.
Cheers!
Francis,
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
Since this is all new construction I'm also curious to know what you guys think of using 16" OC stud spacing for both wall and ceiling framing.
I've read that using 16" OC is best for lower frequencies and that 24" OC is best for mid-high frequencies. Is that true?
I've also read that in a double stud wall using 16"OC in one wall and 24"OC in the other would help? Is that true?
If anyone can clear that up it would be great so that I could update my plans. I've figured out how to close off the entrance and live room. I'll update the plans shortly.
Cheers!
I've read that using 16" OC is best for lower frequencies and that 24" OC is best for mid-high frequencies. Is that true?
I've also read that in a double stud wall using 16"OC in one wall and 24"OC in the other would help? Is that true?
If anyone can clear that up it would be great so that I could update my plans. I've figured out how to close off the entrance and live room. I'll update the plans shortly.
Cheers!
-
Soundman2020
- Site Admin
- Posts: 11938
- Joined: Thu Aug 21, 2008 10:17 am
- Location: Santiago, Chile
- Contact:
Re: Help with Planning & Building of my Recording Studio
That would work fine.Since this is all new construction I'm also curious to know what you guys think of using 16" OC stud spacing for both wall and ceiling framing.
Not really. In general, if an isolation system works well for low frequencies, it works even better for high frequencies. There is a small advantage to using 24" instead of 16" for low frequencies. However, if you go with 24" OC, then your studs are far apart, so it becomes problematic to mount things on the walls that are less than 24" wide.I've read that using 16" OC is best for lower frequencies and that 24" OC is best for mid-high frequencies. Is that true?
No!I've also read that in a double stud wall using 16"OC in one wall and 24"OC in the other would help? Is that true?
- Stuart -
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
Excellent! Thanks Stuart!
I kind of figured that if you can build a system that isolates low frequencies well that it would take care of mids and highs.
I'll update my plan and finish adding the individual ceilings using 16" OC
I kind of figured that if you can build a system that isolates low frequencies well that it would take care of mids and highs.
I'll update my plan and finish adding the individual ceilings using 16" OC
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
I've been reading more and more on studio designs and recommended room dimensions for studios and I'm not sure how to separate the space I have. This is still the planning stage so I guess I've got some time to figure that out. I’m trying to figure out the best ratios for the control and live room.
The space I have available is 23′ wide by 26′ long. (the room has slopped ceilings 12/12 pitch...one big triangle?). Within that room I’m trying to fit a live room to track drums and other instruments as well as a control room and maybe even a tiny vocal booth. The sketchup plan I posted has the room separated as follows:
- Control room dimensions are 8.8′ width, 12′ length and 12′ high at the highest point in the room. I’m wondering if that’s manageable.
- Live room dimensions are 20′ wide, 14′ length and 12′ high at the highest point.
- Vocal Booth dimensions are 8.8' width, 6.3ft length and approx 8' at the highest point.
I'm pretty sure the Vocal Booth would have to go to give some extra space to the CR but even doing that I'm not sure if that's going to help. Having a triangle shaped room surely limits my options. Taking out the Vocal Booth I could stretch the control room to approx 10/12′ wide by 20′ length if that would be better. That would take away about 1 or 2ft off the length of the live room.
Any thoughts? sorry about all the questions :/ Any help/advice would be greatly appreciated!!
P.S. I can post pictures if needed. I'm getting to a point where I'd like to maybe pay someone to help me figure this stuff out for me. Any ideas as to how much $$ that would cost roughly?
Cheers!
The space I have available is 23′ wide by 26′ long. (the room has slopped ceilings 12/12 pitch...one big triangle?). Within that room I’m trying to fit a live room to track drums and other instruments as well as a control room and maybe even a tiny vocal booth. The sketchup plan I posted has the room separated as follows:
- Control room dimensions are 8.8′ width, 12′ length and 12′ high at the highest point in the room. I’m wondering if that’s manageable.
- Live room dimensions are 20′ wide, 14′ length and 12′ high at the highest point.
- Vocal Booth dimensions are 8.8' width, 6.3ft length and approx 8' at the highest point.
I'm pretty sure the Vocal Booth would have to go to give some extra space to the CR but even doing that I'm not sure if that's going to help. Having a triangle shaped room surely limits my options. Taking out the Vocal Booth I could stretch the control room to approx 10/12′ wide by 20′ length if that would be better. That would take away about 1 or 2ft off the length of the live room.
Any thoughts? sorry about all the questions :/ Any help/advice would be greatly appreciated!!
P.S. I can post pictures if needed. I'm getting to a point where I'd like to maybe pay someone to help me figure this stuff out for me. Any ideas as to how much $$ that would cost roughly?
Cheers!
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
After doing some more reading on CR design I found that a decent Control Room should have a min of 200sq/ft. Is that correct?
Regardless this information sort of forced me to accommodate this into my design and so I've adjusted my plan and as mentioned in my last few posts eliminated the vocal booth and stretched out the CR an extra 16". It's now approx. 123" W x 226" L x 12' H(at the peek of the roof). Doing so gives me a bit smaller Live Room 18.8' W x 12.8' x 12' (at the peek of the roof).
Now I'm starting to do more and more calculations and I have a few questions:
1) After stretching out my current CR design I still only have approx. 192 sq/ft. Is this still manageable for a decent CR? or should I try to stretch even more?
2) Is having a smaller Live Room a bad thing or still manageable? I can try and stretch the CR a bit more to get me up to 200sq/ft + but I just want to make sure that won't effect the LR in a bad way.
I'll post an updated plan later tonight to show the changes.
Thanks,
Francis,
How would I be able to calculate/evaluate modes with a room with slopped ceilings. Most online tools take measurements
Regardless this information sort of forced me to accommodate this into my design and so I've adjusted my plan and as mentioned in my last few posts eliminated the vocal booth and stretched out the CR an extra 16". It's now approx. 123" W x 226" L x 12' H(at the peek of the roof). Doing so gives me a bit smaller Live Room 18.8' W x 12.8' x 12' (at the peek of the roof).
Now I'm starting to do more and more calculations and I have a few questions:
1) After stretching out my current CR design I still only have approx. 192 sq/ft. Is this still manageable for a decent CR? or should I try to stretch even more?
2) Is having a smaller Live Room a bad thing or still manageable? I can try and stretch the CR a bit more to get me up to 200sq/ft + but I just want to make sure that won't effect the LR in a bad way.
I'll post an updated plan later tonight to show the changes.
Thanks,
Francis,
How would I be able to calculate/evaluate modes with a room with slopped ceilings. Most online tools take measurements
-
Soundman2020
- Site Admin
- Posts: 11938
- Joined: Thu Aug 21, 2008 10:17 am
- Location: Santiago, Chile
- Contact:
Re: Help with Planning & Building of my Recording Studio
Well, yes, that's correct. ... Sort of. Yes, the best specs for "critical listening rooms" do specify 200 ft2 as the "minimum", but that does not mean that if you only have 199 ft2 it will be terrible! Nor if you have 190... or 180... or 170... It's a matter of "optimal" and "slightly less than optimal" and "a little worse". A smaller room can still be pretty good... PROVIDED THAT it is designed carefully and treated accordingly. I can design you a 200 ft2 room that sounds terrible, and I can design you a 160 ft2 room that sounds pretty darn good. John has built rooms inside shipping containers! It just gets harder and harder to do as the room gets smaller.After doing some more reading on CR design I found that a decent Control Room should have a min of 200sq/ft. Is that correct?
Yes, bigger is better, for sure, and yes, above 200 ft2 is best (actually, the number is 215.3, because it is specified as 20 square meters....), but your room won't automatically fail if it is smaller.
That's a good size for a room, but did you check the "room ratio" to make sure it is acceptable? Use one of these Room Ratio calculators to figure out the best dimensions for your room:so I've adjusted my plan and as mentioned in my last few posts eliminated the vocal booth and stretched out the CR an extra 16". It's now approx. 123" W x 226" L x 12' H(at the peek of the roof).
http://www.bobgolds.com/Mode/RoomModes.htm
http://amroc.andymel.eu/
Both of those are very good, and will help you to decide how best to build your room. They give you tons of information that is really useful to help figure out the best dimensions.
Warning! You do NOT need to go crazy here, adjusting dimensions to get a "perfect" ratio! There is no such thing. As long as your ratio is not close to one of the "bad" ones, and is reasonably close to one of the good ones, then that's fine. It is more important to have as much volume as possible in the room, than it is to hit the "best" ratio.
Do be aware that the air volume of the LR should be somewhat larger than the air volume of the CR, if possible. One way of looking at it (not strictly accurate, but it helps to get a mental picture), is that you need to hear the "reverb tails" of the LR when you listen on the speakers in the CR. Reverb tails are the lingering remnants of the sound dying away slowly after the cause has stopped: it's the sound of the room itself, to a certain extent, or the sound of how the music reacts with that room, after the music stops. It's the "life" and "character" of the room, what makes it "sound great" for a musician. But it is low level, and dies away at a rate that is proportional to the room volume. Smaller rooms have faster decay. So here's the thing: the decay in your CR will be "neutral": just right for the room itself. You will tune it that way, because control rooms MUST be neutral: They must not add to nor subtract from the natural direct sound. So if it turns out that the reverb tails in your LR are about the same length as the natural decay time of the CR, you won't hear the reverb tails! When you listen on your control room speakers, you'll hear the natural decay of the CONTROL ROOM, since it will be louder than the reverb tails from the LR in your recording. The tails in the LR need to be substantially longer than the decay time of the CR, so that you can hear those reverb tails in the CR, after the natural decay has already gone by... and you are left hearing the sound of the LR. If your rooms are about the same size, then you'll be challenged to hear what the music really sounds like in the LR, as you listen in the CR.... but the guy listening to your mixes on ear buds, where there is no room at all and zero decay time, will hear everything! Including stuff that you never heard in your mixes...Doing so gives me a bit smaller Live Room 18.8' W x 12.8' x 12' (at the peek of the roof).
So the ideal is to have the LR larger than the CR, and if you can't do that, then make the LR slightly more "live" (longer tails) and the CR slightly more dead (shorter decay time), by using the correct treatment in both rooms.
That's fine! As I mentioned above, 200 ft2 is not a sharp cut-off point: it's just a rough marker that shows where performance starts to tail off for smaller rooms. Think of it sort of like the "roll off" in bass response for a good speaker: The speaker spec might say that it goes down to 35 Hz, but that doesn't mean that it produces no sound at all at 34 Hz! It just means that at 34 Hz, the sound is a tiny fraction less than it should be, optimally. And at 33 Hz, it's a little less optimal. Even at 30 Hz, and 25 Hz, the speaker is still putting out some sound. The 35 Hz spec just shows the point where things START deteriorating: It's not a sharp line. Ditto for the 200 ft2 "spec": it's just a rough point where things start rolling off.1) After stretching out my current CR design I still only have approx. 192 sq/ft. Is this still manageable for a decent CR? or should I try to stretch even more?
See above: As long as it as larger VOLUME of air than the CR, that's fine. And you can also adjust the treatment of both rooms a little, pushing the LR a bit more to the liver / longer tails side, and damping the CR a little more than it should be.2) Is having a smaller Live Room a bad thing or still manageable?
In some design concepts for control rooms, there's the concept of the ITDG, or Initial Time Delay Gap. That's the small period of time between the instant where your ears hear the direct sound from the speaker, and then hear the first "echo" of that direct sound, that has bounced off some wall somewhere, and come back to your ears. The specs for control rooms often say that the first "reflected" sound should not arrive until at least 20ms after the direct sound, and that when it DOES arrive at your ears, it should be diffuse (not specular), and during that time, the intensity should be at least 20 dB lower than that direct sound. That "20 ms window" is the ITDG. After than time has passed, some specs call for the level to increase again, above -20 dB, then die away slowly. So if you look at a graph showing how the room responds to an "impulse" (a sudden very loud, very short sound, such as a balloon popping), you'll see a tall spike as you hear the direct sound of the pop itself, then nothing for 20ms (or at least, nothing louder than -20db), then you'll start to see the level rise again as the diffuse sound of the balloon pop that has bounced around the room and been absorber and diffused, starts to get back to your ears, at maybe -15 dB or so, but then it dies away slowly for a few hundred milliseconds, until it is completely gone. That "space" where you hear "nothing" after the initial direct sound, is the ITDG: The Initial Time Delay Gap between the direct sound hitting your ears, and the reverberant field hitting your ears.
So, the ITDG has to be long enough to allow you to hear the sound of the LIVE ROOM reverberant field, which hopefully does not have an ITDG, or has a short ITDG, or one that does not go below -20 dB. As long as you have that condition, then you will be able to hear the "sound" of the live room when you listen on the CR speakers. But if your CR has an ITDG that is too short, or too loud (above -20dB), or if the level rises up too high again after the ITDG, then you won't hear those small hints from the LR room sound, in the CR. In that case, it is better to not have a rise above -20 dB after the ITDG: just keep the level low, say -30 dB for the ITDG, don't allow it to rise again above that, then the decay can start after that, at a lower level. That's what I do for small control rooms and small live rooms. It's not easy to get it right, but it does give you a better shot at hearing the subtle delicacies of the LR reverb tail, in the CR.
OK, so some people think this is splitting hairs, since LR tails are low level and subtle in any case, so there's no point in caring about them much. They don't think that "tails" are important at all. Maybe if you only ever plan to record shrieking grunge rock, or mind-mashing heavy metal genres, that scream through the entire song at 120 dB without it ever being possible to have the slightest hint of a reverb tail, then that's OK. But if you plan to record music that has a bit of feeling to it, with subtleties, nuance, ambiance, then this is very important. (And if you only ever plan to record screeching, howling, wailing, bellowing heavy metal, then why bother with a studio at all?? You could record that in a subway station, and not even notice the trains roaring past . . .
Not necessary. At 190 ft2, you are within the ball park for having a decent control room. Yes, bigger would theoretically allow slightly better, but the difference is not huge, and 190 is still good.I can try and stretch the CR a bit more to get me up to 200sq/ft + but I just want to make sure that won't effect the LR in a bad way.
Simple answer: you can't! Room mode calculators only work for perfectly rectangular rooms. More complete answer: You can still use the calculators to get a good idea of how the room will behave, as long as the angle is not too great, and as long as you understand what you are looking at.How would I be able to calculate/evaluate modes with a room with slopped ceilings.
For example, if it is JUST the ceiling that is off, and your walls are still parallel and perpendicular, then the predictions for axial modes in the length and width directions will still be perfectly correct, and so will the predictions for tangential modes that only involve the four walls. But axial mode predictions related to the ceiling will NOT be correct, and neither will predictions for tangential modes that involve the ceiling, or any oblique modes. However, if only part of the ceiling is sloped (eg, the front half rises, but the rear half is flat), then the predictions will still be valid for the part of the room where the ceiling is not sloped. And it the angle of slope is not huge, then the predictions will not be far off, and you can still use them, as long as you realize that they won't be entirely accurate.
The big issue happens when you have a room that has more than six sides, or when the splay angles on the walls and ceiling are large. The more complex the room is, and the further it is from being a pure rectangle, the less accurate the prediction will be.
Having said all that, you do NOT need to go crazy trying to find the perfect ratio for your room! There is no such thing anyway, and it doesn't really matter all that much, as long as you stay away from the bad ratios. So for example, if you have to reduce the length of your room by 6" to get a good ratio, then don't do it! It's better to have that extra six inches to increase the room volume. The only time I'd do that is if the room was a perfect cube, and the only way I could fix it was by reducing the length or width a bit. And even then, if it was a very small room, I would be very hesitant to take off those 6". For a large room, it would not be a problem to lose 6"... but then again, for a large room there would be no need to lose 6" anyway, since large rooms already have better acoustics than small rooms!
- Stuart -
-
Studio45
- Posts: 97
- Joined: Thu Feb 04, 2016 12:47 am
- Location: Ontario, Canada
Re: Help with Planning & Building of my Recording Studio
As always thanks for your prompt response Stuart! Hope you had a great xmas!!
About the room ratio calculator, I just want to confirm based on the information you provided. I've attached a sample picture of the sketchup plan and as you can see the ceilings are slopped at 45 degrees (12/12 pitch) but there are no additional angles. I suppose you can say that there are a total of 6 sides.
So to recap:
1) In my case the room mode calculator will only work and predict axial modes in length and width directions as well as tangential modes for the four walls. Correct?
2) Based on the attached picture it doesn't seem like the tool would work because of the small amount of the front and rear wall will be flat. Correct?
3) On the bright side I suppose I can use the wasted space in the back of the CR for bass-trapping even though it wouldn't go all the way up to the ceiling?
Because of the slopped ceiling if I was to walk to the back of the room until my head would hit the ceiling/wall I'd have about 5-6 feet of wasted space I can't use other than for storage or most probably some sort of absorption/treatment.
4) I'll be honest and say that I haven't done enough research to fully understand the data I'm looking at when using the Room Mode Calculators but from what I understand, it seems I shouldn't waste too much time trying to get that perfect ratio since it can most likely be treated afterwards. Correct? Regardless I will read through Rod's book again and try to make sense of Modes and what to watch out for. For the most part I think the current size/layout will be okay.
With the dimensions I've currently designed this is information that was returned from the tool:
-------------------------------------------------------------------------------------
Room Dimensions: Length=18.82 ft, Width=10.25 ft, Height=12 ft
Room Ratio: 1 : 1.17 : 1.83
R. Walker BBC 1996:
- 1.1w / h < l / h < ((4.5w / h) - 4): Fail
- l < 3h & w < 3h: Pass
- no integer multiple within 5%: Pass
Nearest Known Ratio:
- "24) A worst case scenario calculated by RPG" 1 : 1.075 : 1.868
RT60 (IEC/AEC N 12-A standard): 234 ms
- ±50ms from 200Hz to 3.5kHz = 184 to 284ms
- ±100ms above 3.5kHz = 134 to 334ms
- <+300ms at 63hz = 534ms
- 300<RT60<600ms
RT60 (ITU/EBU Control Room Recommended): 217 ms
- ±50ms from 200Hz to 4kHz = 167 to 267ms
- <+300ms at 63hz = 517ms
- 200<RT60<400ms
Absorbtion to achieve ITU RT60: 522 sabins
Volume: 2316 ft^3
Surface Area Total: 1082 ft^2
Surface Area Floor: 193 ft^2
Surface Area Ceiling+Floor: 386 ft^2
Surface Area Front Wall: 123 ft^2
Surface Area Front and Rear Wall: 246 ft^2
Surface Area Left Wall: 225 ft^2
Surface Area Left and Right Wall: 450 ft^2
Surface Area 4 Walls: 696 ft^2
Surface Area 4 Walls + floor: 889 ft^2
(sabins - front wall - carpet) / Left+Right+Rear wall: 35 %
(sabins - front wall) / Left+Right+Rear wall: 69 %
Schroeder Fc: 108hz
Frequency Regions:
- No modal boost: 1hz to 30hz
- Room Modes dominate: 30hz to 108hz
- Diffraction and Diffusion dominate: 108hz to 432hz
- Specular reflections and ray accoustics prevail: 432hz to 20000hz
Count (30-193hz) : Axials=13, Tangentials=54, Obliques=72
Count (30-100hz) : Axials=6, Tangentials=6, Obliques=2
Critical Distance (direct = reverberant field): 14.60ft
----------------------------------------------------------------------------------------------------------------------
Back to reading Rod's Book! Once I get some sort of confirmation on my dimensions and layout I'll update my plan and start looking at HVAC silencer boxes, supply and return locations.
Again, thanks for all your help! And please let me know if you'd like to see additional angles or screenshots of the plan.
Happy New Years everyone!
Cheers!!
This is good news for sure because I was starting to have doubts. I certainly want to try to design the CR as best as possible.That's a good size for a room, but did you check the "room ratio" to make sure it is acceptable? Use one of these Room Ratio calculators to figure out the best dimensions for your room.
About the room ratio calculator, I just want to confirm based on the information you provided. I've attached a sample picture of the sketchup plan and as you can see the ceilings are slopped at 45 degrees (12/12 pitch) but there are no additional angles. I suppose you can say that there are a total of 6 sides.
So to recap:
1) In my case the room mode calculator will only work and predict axial modes in length and width directions as well as tangential modes for the four walls. Correct?
2) Based on the attached picture it doesn't seem like the tool would work because of the small amount of the front and rear wall will be flat. Correct?
From looking at the attached image, would you consider this a "complex" room? It will have a total of 6 sides but obviously the angle of the ceilings is pretty big.The big issue happens when you have a room that has more than six sides, or when the splay angles on the walls and ceiling are large.
3) On the bright side I suppose I can use the wasted space in the back of the CR for bass-trapping even though it wouldn't go all the way up to the ceiling?
Because of the slopped ceiling if I was to walk to the back of the room until my head would hit the ceiling/wall I'd have about 5-6 feet of wasted space I can't use other than for storage or most probably some sort of absorption/treatment.
4) I'll be honest and say that I haven't done enough research to fully understand the data I'm looking at when using the Room Mode Calculators but from what I understand, it seems I shouldn't waste too much time trying to get that perfect ratio since it can most likely be treated afterwards. Correct? Regardless I will read through Rod's book again and try to make sense of Modes and what to watch out for. For the most part I think the current size/layout will be okay.
With the dimensions I've currently designed this is information that was returned from the tool:
-------------------------------------------------------------------------------------
Room Dimensions: Length=18.82 ft, Width=10.25 ft, Height=12 ft
Room Ratio: 1 : 1.17 : 1.83
R. Walker BBC 1996:
- 1.1w / h < l / h < ((4.5w / h) - 4): Fail
- l < 3h & w < 3h: Pass
- no integer multiple within 5%: Pass
Nearest Known Ratio:
- "24) A worst case scenario calculated by RPG" 1 : 1.075 : 1.868
RT60 (IEC/AEC N 12-A standard): 234 ms
- ±50ms from 200Hz to 3.5kHz = 184 to 284ms
- ±100ms above 3.5kHz = 134 to 334ms
- <+300ms at 63hz = 534ms
- 300<RT60<600ms
RT60 (ITU/EBU Control Room Recommended): 217 ms
- ±50ms from 200Hz to 4kHz = 167 to 267ms
- <+300ms at 63hz = 517ms
- 200<RT60<400ms
Absorbtion to achieve ITU RT60: 522 sabins
Volume: 2316 ft^3
Surface Area Total: 1082 ft^2
Surface Area Floor: 193 ft^2
Surface Area Ceiling+Floor: 386 ft^2
Surface Area Front Wall: 123 ft^2
Surface Area Front and Rear Wall: 246 ft^2
Surface Area Left Wall: 225 ft^2
Surface Area Left and Right Wall: 450 ft^2
Surface Area 4 Walls: 696 ft^2
Surface Area 4 Walls + floor: 889 ft^2
(sabins - front wall - carpet) / Left+Right+Rear wall: 35 %
(sabins - front wall) / Left+Right+Rear wall: 69 %
Schroeder Fc: 108hz
Frequency Regions:
- No modal boost: 1hz to 30hz
- Room Modes dominate: 30hz to 108hz
- Diffraction and Diffusion dominate: 108hz to 432hz
- Specular reflections and ray accoustics prevail: 432hz to 20000hz
Count (30-193hz) : Axials=13, Tangentials=54, Obliques=72
Count (30-100hz) : Axials=6, Tangentials=6, Obliques=2
Critical Distance (direct = reverberant field): 14.60ft
----------------------------------------------------------------------------------------------------------------------
Back to reading Rod's Book! Once I get some sort of confirmation on my dimensions and layout I'll update my plan and start looking at HVAC silencer boxes, supply and return locations.
Again, thanks for all your help! And please let me know if you'd like to see additional angles or screenshots of the plan.
Happy New Years everyone!
-
Soundman2020
- Site Admin
- Posts: 11938
- Joined: Thu Aug 21, 2008 10:17 am
- Location: Santiago, Chile
- Contact:
Re: Help with Planning & Building of my Recording Studio
Ooops! Room mode calculators are not applicable here, except for the length axial mode, and perhaps slightly for the width.About the room ratio calculator, I just want to confirm based on the information you provided. I've attached a sample picture of the sketchup plan and as you can see the ceilings are slopped at 45 degrees (12/12 pitch) but there are no additional angles. I suppose you can say that there are a total of 6 sides
Length yes, width... not so much. Only to a limited extent, since most of the side "walls" is steeply angled. There's only a small part that is vertical.1) In my case the room mode calculator will only work and predict axial modes in length and width directions as well as tangential modes for the four walls. Correct?
Yep!From looking at the attached image, would you consider this a "complex" room?
I think we are talking about "front / back" and "sides" in different senses here! For me, the best way to lay out a control room in that space, would be to face the window. So the "front" would be the window, the "back" would be the door, and the "sides" would be the deeply sloped ceiling.3) On the bright side I suppose I can use the wasted space in the back of the CR for bass-trapping even though it wouldn't go all the way up to the ceiling?
Right! Especially with that shaped room, where the calculator isn't going to help too much anyway.4) I'll be honest and say that I haven't done enough research to fully understand the data I'm looking at when using the Room Mode Calculators but from what I understand, it seems I shouldn't waste too much time trying to get that perfect ratio since it can most likely be treated afterwards. Correct?
- Stuart -