Ok, I am still waiting for answers from my last post, but will move forward and perhaps focus on a different problem for a little while. Again, I have not started the build yet, so still very much in research mode!
Back on to HVAC: I have had a couple of guys round re air-conditioning and ventilation this week to look at the garage and to suggest ideas. They aren't studio experts at all, just local air-con companies, but one has experience working in a school recording studio environment recently. However, I'm keen to make sure I know what im talking about when requesting quotes etc.
Stuart (or anyone else out there) - Here's where I'm at:
So figure the volume of the room (in cubic meters or cubic feet) multiply by the number of changes per hour, and that's your flow rate: you need a fan that can move that much air per hour. Fans are normally rate as being able to move X-many Cubic Feet per Minute (CFM) of air, so look for fans that can move your amount of air.
I have worked out my inner room volume (L:4.8m x W: 2m x H: 2.3m) = 22m3.
If I go for 5 room changes per hour then I need a fan that can move 22m3 x 5 room changes per hour = 110m3.
With this worked out I can divide by 60 minutes (110m3 x 60 minutes) to work out how much air to be moved per minute = 1.8m3.
So i need a fan that can move 1.8m3 per minute.
But that's not all! Fans only produce their rated air flow in free air, with no duct: put them in a ducted system, and the flow rate drops, depending on how much "static pressure" the system has, which basically means how much it resists the flow of air through it. So you have to calculate that, and find a fan that can move that much air at the estimated static pressure of your ducting system and room. For example, a fan might be rated at 250 CFM, but only be able to move 180 CFM with a static pressure of 0.5". So be careful there: do the math, and get the right fan. If you overload a fan with too much static pressure, it will not only not move enough air, but will be much noisier, use more power, be less efficient, and burn out sooner.
Then, with all that figured out, you need to do the calculations to figure the duct size: you want the air flow speed to be less than 300 feet per second (fps) where it leaves the register. Since you already know how many cubic feet per minute you need, and how many feet per second you need, it is now simple math to find out how many square inches of cross section you need for your ducts.
This is where I'm struggling a little. Here we talk about understanding the static pressure of the system and I assumed this to mean - the resistance caused by using the fan within a ducted system, correct? However, we then talk about later working out the duct size required to achieve the relevant air flow speed, but this confuses me as I thought we had already considered duct size when working out static pressure? Sorry if I sound stupid.
I guess what I am asking is: How do I work out both the required duct size and static pressure in order to choose the relevant fan size/power. What are the sequential steps to working this out?
I'm thinking that one single fan will be enough for my build blowing fresh air into the studio, with just a 'stale-air-out' vent (without a fan) where stale air will be forced out. This system together with a small mini-split air con system. If this sounds ok, I assume the 'stale-air-out' vent route will not require silencers?
Any help would be great.
Regards
Marc