If there was a layer of concrete (almost purely reflective material) wrapped around the 4 inches of fiberglass, this would have no influence on what is bounced back into the room,
Of course it would, because that's how the test is done! The test chamber is basically a concrete bunker, highly reverberant across the entire spectrum, down to lowish frequencies. It can only conduct tests down to the frequency where the room no longer has a statistical reverberant field, because obviously, trying to measure revbereance where there is none would be silly. (Just like trying to play drums in a room that does not have a reverberant field at the frequencies where drums need it, for example). So the test chamber has to be large in order to be able to actually have a response at lowish frequencies (in other words, the walls have to be far enough apart that there can be multiple modes at all frequencies of interest), and the room as to be highly reverberant, built with very solid, very massive, very rigid, very reflective walls, floor and ceiling. The best material for doing that, is concrete.
One test is done with the room totally empty, to record the reverberant response of the room all by itself, then the sample is placed on the floor of the room, covering enough area to produce a usable response, and the test is repeated, to see what changed. The difference between the two tests is used to do the calculations that then end up as the coefficients of absorption.
So since the test itself is done with the sample sitting on the concrete floor, then the test results do, in fact, depend on reflections from the floor. The floor has a large influence on the results. If there were no floor at all under the sample (levitated in mid air), then there would be no reverberant field to measure, either with or without the sample! The floor is partly responsible for CREATING the reverberant field, so it has an enormous influence on the results.
(That said, there are several test protocols among the ASTM C423 standardized procedure for this, and some of them do allow the sample to be placed a certain distance away from the floor. the E-405 notation, for example, is for testing the sample when there is an air gap of 405 millimeters between the sample and the floor, while the "A" notion is for having the sample directly on the floor, with no air gap at all. So do mae sure you are comparing apples to apples when looking at absorption coefficients. E-405 causes the sample to appear to absorb down to lower frequencies than A.)
Essentially the sound (in worst case) has 2 trips through an absorption material in a practical room.
Correct, yes, but don't forget that this is a reverberant field we are talking about here, fully diffuse, fully even, so there are multiple paths that sound takes through the sample, each one at a different angle and of a different path length. The shortest path is for normally incident sound, and the longest path is for grazing incidence.
If it hits a purely reflective material just outside the absorption then its 1 trip going in, and 1 trip coming back?
In theory, but it could be more if there are internal reflections taking place inside the sample, due to impedance mismatches or diffraction, or refraction, or whatever. The minimum number of paths that any sound could take is one, and there's really no limit on the maximum number. But assuming that each wave takes about 2 trips is about right.
And still this chart would say it is still purely absorptive and in practice?
No, it is not purely absorptive. The coefficients do not mean that. A coefficient of one simply means that the sample showed the exact same behavior as an equivalent sample that has 1 sabin of absorption would show, at that frequency. There is no such think as "purely absorptive", just as there is no such thing as "purely reflective".
This would measure an RT60 of 0
No. An RT60 time of zero is impossible, since that would imply that the sound wave was actually moving at the speed of light!

It takes a certain finite time for the sound wave to get through the sample, and get back out again. That time depends on many factors, including the speed of sound in the air inside the room, the speed of sound inside the sample (which will practically always be slower than in air, since the sample itself changes the way air deals with heat from adiabatic to isothermic), the path length in air, the path length in the sample, etc. There will always be a finite RT60 time for any room that has walls around it. RT60 = 0 implies that no time at all passed from the instant the sound wave was generated until it was completely gone, and of course that is impossible. Air itself makes that impossible. There will always be a reverberant field in any room, and all that you are measuring with these tests is how the sample changed that reverberant field.
Would this mean that if the absorption material was doubled (now 8 inches) it should completely absorb AS WELL AS completely isolate it from outside?
Nope! Because there is no such thing as "completely absorbed", and you still have not grasped that this testing method does not even test absolute absorption! It only tests absorption
COEFFICIENTS , and even then only with reference to a theoretical reference sample of 1 sabin.
In other words, you are not measuring how fast your car is ACTUALLY going, relative to the road. You are measuring how much faster or slower it is going than a hypothetical "standard" car would go on the same road. That's all. The test tells you nothing at all about the road, or your absolute speed. Only the difference in speed relative to another car.
So if you wanted to know how an 8" thick sample behaves, then you would have to take such a sample into the test chamber, and test it.
or is there no connection there?
No, there is no direct connection.
Ok, can we consider for a second the 4 inch Fiberglass Coefficients from Sayer's chart
I prefer to look at the actual measured data published by the manufacturers, as tested in independent, reputable acoustic testing facilities. Here's such a table from Owens Corning, about there 700 product line:
OC-703-specs.jpg
That comes from page 26 of the rather complete design guide that Owens Corning has published, regarding their products for acoustic wall insulation.
(which what fiberglass is this referring to by the way?
Generic fiberglass, I assume. A very rough approximation, taken from many sources.
seems better than the chart you posted on 703)
I posted a graph, not a chart, since it is often easier to interpret when you have a clear visual representation. I provided one single graph for one single product to illustrate the point that it is entirely possible and valid and correct to have coefficients greater than 1. I did not post anything else, since it was not necessary to illustrate that specific point. But if you want more complete data about a whole bunch of spe, Bob Golds has a very complete set on hos website:
http://www.bobgolds.com/AbsorptionCoefficients.htm That's the best compilation of data that I know of, currently.
So the perspective of the coefficient chart has more to do with what is bounced back into the room, rather than what escapes?
No. It has to do with the absorption of specific third-octave frequency bands as compared to the theoretical absorption of an equivalent area of a hypothetical sample that provides 1 sabin per square meter of absorption.
It's a hard concept to get your head around, I know. And very confusing! But it you think this is complex, wait until you try to understand coefficients of diffusion...
- Stuart -