whitelion88 wrote:Do room modes (room shape) have any effect the STC rating of a room or do room modes only have an effect the acoustics within the room itself?
In other words, all other things being equal, if I build a room with non-parallel walls and then build the same size (in terms of square feet) room with a rectangular shape, will one have a different STC rating than the other?
While I know this can look as bean counting versus the other contributors, there is some logic in your question.
Since one compares the diffuse field level (several methods can be applied) in one room with the same in the other room (for normal STC lab tests), modal behavior can certainly influence the real live STC.
Even the volume of the receiving room can influence STC (mainly in the low frequencies).
What's wrong in your assumption is that non-parrallel walls should not show modal behavior in the room. Hence it all depends on circumstances. if you have modes in your room which coincide with the mass-spring of your walls then you can be in trouble.
At studiotips long time ago there was a typical situation where a room mode DID coincide with this mass-spring resulting in a wall which acted as a filter.
ASTM E 413 – 04
Classification for Rating Sound Insulation
4. Significance and Use
4.1 These single-number ratings correlate in a general way with subjective impressions of sound transmission for speech, radio, television, and similar sources of noise in offices and buildings. This classification method is not appropriate for sound sources with spectra significantly different from those sources listed above. Such sources include machinery, industrial processes, bowling allies, power transformers, musical instruments, many music systems, and transportation noises such as motor vehicles, aircraft and trains. For these sources, accurate assessment of sound transmission requires a detailed analysis in frequency bands.
Note here that the standard itself refers to its limitations in function of types of noise sources.
7. Keywords
7.1 architectural acoustics; building design; ceiling attenuation class (CAC); field sound transmission class (FSTC); noise isolation class (NIC); normalized noise isolation class (NNIC); partitions (buildings); sound insulation rating; sound transmission class (
STC)
ASTM E 90 – 04
Laboratory Measurement of Airborne Sound Transmission Loss of Building Partitions and Elements
1. Scope
1.1 This test method covers the laboratory measurement of airborne sound transmission loss of building partitions such as walls of all kinds, operable partitions, floor-ceiling assemblies, doors, windows, roofs, panels, and other space-dividing elements.
1.2 Laboratory Accreditation—A procedure for accrediting a laboratory for performing this test method is given in Annex A3.
6. Test Rooms
A lot of conditions must be fulfilled (too much to copy here & copyright issues) but a few short (incomplete) things:
Source and receiving room >= 50 m3 (1765 cft)
Rooms must be diffuse (diffusers)
Rooms must be below a max allowed absorption.
Average Temperature in rooms for walls 22 +/- 5° C.
6.2.3 During the sound pressure level and sound absorption measurements, variations in temperature and humidity in the
receiving room shall not exceed 3°C and 3% relative humidity respectively. Temperature and humidity shall be measured and
recorded at the beginning and end of each test to ensure compliance.
This isn't complete. It just gives an idea that
STC is a value within certain boundary conditions. And more than atmospheric conditions, which don't differ that much in common applications, modal behavior and receiving side volume will influence practical
STC values.
While not obliged, certain labs therefore will or can measure in both directions and average these values, since THEORETICALLY (not taking flanking effects into account) transmission loss is reversible. And take into account that such rooms and the measurement methods are designed to exclude at a maximum such disturbing phenomena.
The question of the OP isn't that illogical, with this exception that he starts from the wrong assumption that non-parallel walls should prevent or avoid room modes.