FINISHED IN 2020! Sharward's Partial Garage Conversion

Discuss studios designed and built by others.

Moderators: Aaronw, John Sayers

Sword9
Posts: 219
Joined: Mon Aug 30, 2004 11:46 am
Location: Nashville, TN

Post by Sword9 »

I was wondering when someone around here would start talking about the Kinetics floor systems. A studio designer I used to work for used this almost exclusively for his floating floors. For small rooms especially, this seems like the most pain-free install there could be.
SaM Harrison
Location Engineers
Nashville, TN
cadesignr
Senior Member
Posts: 566
Joined: Mon Mar 03, 2003 4:25 pm
Location: Oregon USA

Post by cadesignr »

Me too. I hardly ever see mention of it as a solution. Although, I just did in another thread below. At least a roll out type.
fitZ
alright, breaks over , back on your heads......
sharward
Moderator
Posts: 4281
Joined: Mon Jan 03, 2005 4:08 pm
Location: Sacramento, Northern California, USA
Contact:

Responses to Everyone

Post by sharward »

What a relief -- I know what direction to go in and I'm going in it. Ahhhh, to be unstuck (again). 8)

We're at 7 pages on this thing and over 4,000 page views -- seeing these numbers and the thoughtful responses are really encouraging. Not only am I not alone in this, but I'm helping others avoid the same pitfalls. In short, by helping others, I help myself at the same time. :)

Many have contributed in the past week and my responses (if any) have been weak. Here are answers to your questions, acknowledgements of ideas, blah blah blah...
mikeklooster wrote:just a thought, but check this http://www.kineticsnoise.com/arch/rimconcrete.html and http://www.kineticsnoise.com/arch/flm.html. These floors might be expensive, but they are simple and might have the correct documentation.
You know how sometimes the answer is right in front of you and you just can't/won't see it? Well, it looks like you nailed it, Mike, so you get the prize for suggesting it first! :D I had taken the EPDM ball and ran with it, assuming it was the way to go, and in the process I (obviously) turned a blind eye to the other solutions. (At the defense of EPDM, it is still a way to go, but the lack of documented specs makes using that method impractical in terms of meeting some municipal inspector scrutiny.)
. . . you have to reach for the impossible, and then accept the acheivable. The closer you get to impossible, the higher the acheivable gets.
I have read those words several times over the past few days, and each time I read them, they become more meaningful to me. 8)
. . . get those drums out of their bags and start remembering why you decided to spend your time reading about drywall.
:lol: You're so right, Mike -- in fact, after weeks of constant badgering by a few coworkers, I'm finally going to bite the bullet and join Skip's Music's Weekend Warriors next weekend! I'll probably be one of the youngest guys in the program, but it promises to be a lot of fun while not consuming so much time that I can't get some good drywall reading time in. ;)

Now, onto Steve's stuff...
knightfly wrote:I get the impression that Auralex has done little (if any) actual testing on their floor floating materials; otherwise there would be more technical info available on their site - customer education is almost NEVER a BAD thing, unless you're selling "snake oil".
Yes, I agree. I'm not going to go so far as to say they're selling snake oil (and I realize you're not necessarily saying that either), but I will say that they seem to have something in common with the snake oil people in that there's not sufficient data made available to (1) prove that their products actually work as advertised and (2) convince building department bureaucrats worldwide that they're structurally safe and reliable.

Hopefully they're plugged into this thread and will benefit from this feedback... Or they can prove that we're incorrect. Either would be good.
. . . you could get better results by going with a more commercial method; i.e. using kinetics or mason ind. spring jacks under a 6" CONCRETE floated slab. Advantages; lower floor level overall, more mass, less BS trying to lay bricks and mortar evenly, full architectural specs available, adjustable for sag AFTER the fact, MUCH quicker install...
Agreed: commercial method now officially adopted. [gavel slam]
If I'd remembered just how obdurate most BRA's can be, I would have tried harder to talk you out of your brick floor - for one thing, brick isn't as high mass (usually) as concrete, for another once this is in place I doubt seriously whether you will EVER actually "dig up" a section - for another, being able to lower your floor level and still get maximum isolation HAS to be a plus.
Well, the fact is, if I go with a solution that is tried and tested and has bulletproof specifications, then the likelihood of having to do a major repair or adjustment underneath the floor is greatly mitigated, if not completely eliminated. In short, if there are no rubber feet, there are no rubber feet to fix. Amen to that!
Dan ''The Man'' Fitzpatrick wrote:. . . you only recently went to the planning commission and started to feel your way around. you didn't think they were just going to stamp OK on your plan did you?? :P
:lol: Exactly! What I really hoped to find out is whether I needed to provide more details in the form of calculations (such as load distributions, span table excerpts, etc.) for some of the construction. Although I knew there was always a possibility that they'd want to shut it down for one reason or another, the "landing" thing really surprised me, and I honestly didn't expect it would be so impossible to provide meaningful specs on the EPDM.
One other idea ... get out your wallet and say, "maybe my friend mr. washington can persuade you ..."
:lol: I just about fell on the floor when I read that! :lol: CLASSIC. 8)

Thanks for all your other thoughts and suggestions, Dan. Since I'm no longer pursuing a method that isn't well documented by official sources, hopefully I won't have to go to the lengths you proposed. :)
knightfly wrote:http://kineticsnoise.com/arch/tests/pdf/A13-b.pdf

See table 6 - this is 4" concrete floated on RIM. Note the 9 dB improvement @ 80 hZ of the concrete vs. wood. Mass rules down here.
Great stuff.
50 dB TL @ 80 hZ would equate to a room volume level (drums) of at least 95 dB in the room, before it would be even slightly audible outside.

Add background levels outside, and someone standing right beside your wall might be able to tell you were playing drums inside, but only barely...
:D
If you upped the concrete to 6" (with appropriate changes in RIM material) those figures would improve by about 3 dB at the low end -
If I'm going to go through all the effort to do 4", why not add the extra 2" for better isolation -- right?
looks like 6" concrete/ply/RIM system would run you about $1200 (no labor, but includes cost of concrete + plywood) . . .
Hey, that won't break the bank -- and not having to lay all those bricks won't break the back! 8)
You would need to level the floor though; no practical way of putting "legs" under it. Don't know what self-leveling concrete would add to cost, you might check locally on that??!?
Yes, I've been thinking a lot about this over the past couple of days.

My garage floor is essentially level in the "panhandle" (rear left) area, and then it slopes about ¼" per foot. This means that a straight board laid on the floor from back to front would have a fulcrum near the middle.

As far as laying the Kinetics RIM material and the plywood goes, that shouldn't be much of a problem -- I can run a seam along the point where the slope starts. However, building a concrete form with an uneven bottom may be a little challenging. I'll probably have to lay an oversized board onto the floor and snap a level chalk line, then use a circular saw to trim off the excess...? Or maybe I can see if the retired gentleman down the street from me with a wood shop in his garage would be willing to make a few cuts for me...?

Thanks again, everyone.

Removed INCORRECT illustration so that it doesn't confuse people
Last edited by sharward on Mon Apr 25, 2005 3:26 am, edited 3 times in total.
sharward
Moderator
Posts: 4281
Joined: Mon Jan 03, 2005 4:08 pm
Location: Sacramento, Northern California, USA
Contact:

Slab Crack?

Post by sharward »

In another thread, cadesignr wrote:My own experience with building a HEAVY wood floating floor on an existing "4 concrete slab ended up cracking it.
Hey Fitz -- should I be concerned about this? (I'm thinking YES. :shock: )
cadesignr
Senior Member
Posts: 566
Joined: Mon Mar 03, 2003 4:25 pm
Location: Oregon USA

Post by cadesignr »

I'm finally going to bite the bullet and join Skip's Music's Weekend Warriors next weekend!
8) :lol: I'm a veteran of the Skips Music Weekend Warrior WARS!! :P We won. I took no captives. Pure EXTREME PREJUDICE!! Hahahaha! Have fun Kieth! BTW, say Hi to Skip. I worked at
Skips store for three years.
Hey Fitz -- should I be concerned about this? (I'm thinking YES. Shocked )
Well, Kieth I don't know. The slab that I had my floor on was an OLD seperate garage, that was in a low spot in the field out behind the house. Looked like maybe water had formed around the slab numerous times from flooding. It might have cracked from areas under the slab being washed away or maybe settleing. Your garage is new, contractor built, designed for a car(probably heavier wire grid) and a gravel bed. But you never know. I would think it would be ok with your weight distribution, but it might be wise to consult someone with real engineering knowledge, since you are putting brick on the floor. Not much lighter than a floating concrete slab with all the wood support I would think. Anyway, thats why I mentioned it in the other thread. This is AFTER the fact design, as far as the slab is concerned, and it MAY not handle it. I hope someone DOES know and can tell you for sure. Sorry. I do know this though. This is a complete room with a heavy floor, and even small buildings with the same proportionate weight are usually required to have a perimeter footing at least TWICE as deep as your slab probably is. Maybe more, I don't know what code calls for. Maybe BID can tell you. Thats the best I have to offer.
I've often wondered about this though, and even mentioned it on a few forums, but no one ever responded with a negative experience. One person who is an engineer agreed with me once though. That tells me something.
fitZ
added later:
:roll: HOLY CRAP. Just read the whole previous thing about using 6" concrete floating floor.....er...I think :? Is that what you are doing...hmmm. Boy, things change fast around here :lol: Hey Kieth, I see you found out what I meant about Sac BID :wink:
alright, breaks over , back on your heads......
sharward
Moderator
Posts: 4281
Joined: Mon Jan 03, 2005 4:08 pm
Location: Sacramento, Northern California, USA
Contact:

Post by sharward »

cadesignr wrote:. . . BTW, say Hi to Skip. I worked at Skips store for three years.
Will do!
Your garage is new, contractor built, designed for a car(probably heavier wire grid) and a gravel bed.
All true. Not only do I have the advantage of having a new (5 year old) home, the builder is big (Beazer Homes) and still doing big business in the area. I also have the cell phone number of one of their Water Intrusion Managers whom I keep in touch with now and then (we became acquainted last summer when a $75,000 plumbing fiasco displaced us for several weeks). An example of the usefulness of this resource: I called him a few weeks ago to ask if the garage floor had a membrane under it, and he instantly answered in the negative. He also assured me, as best he could, that there should be no plumbing under the garage floor.
. . . it might be wise to consult someone with real engineering knowledge . . . I hope someone DOES know and can tell you for sure.
Thanks for the advice, Fitz.
I see you found out what I meant about Sac BID :wink:
Ha! :lol: Well, for what it's worth, I'm not blaming them for the lack of official EPDM testing spec's. Although, the concern about flammability is stupid.

Maybe I'm just fooling myself into thinking that I don't hate their guts just to get through this ordeal.

They just care about public safety and they're not on a power trip.
They just care about public safety and they're not on a power trip.
They just care about public safety and they're not on a power trip.


There. Got it. Really, it's quite blissful! ;)
knightfly
Senior Member
Posts: 6976
Joined: Sun Mar 16, 2003 11:11 am
Location: West Coast, USA

Post by knightfly »

The Kinetics rep for Calif. is in SF; company name is Tempco, and the man to talk to is Dan Hornak - 650-875-6500

Main office contact is Jason Earlich - 1-877-457-2695, Architectural div., X209.

Installed prices for the FLM series (spring, screw jack, poured in slab) runs approx. $12 per sq ft (6" slab), whereas the RIM system runs approx. $6 per sq ft installed; you will need to talk to your LOCAL rep to pin down costs for just materials. Jason didn't recommend the extra expense of the screw jack system for most applications; the RIM system would require extra KIP pads around the perimeter, for that you'll need your weight calculations that the walls/ceiling will add to your floor.

A 5.5" thick concrete slab will weight approx. 66 to 68 PSF without any wood or framing; you already have the weights of your walls and ceiling.

To pour self-leveling concrete (remember you're only leveling the floor at this point; the floated slab comes later.)

Take a straight 2x4 that's at least as long as the uneven part of your floor; set one end on the highest point, then put spacers under the opposite end until a level resting on top of the 2x4 reads dead center.

Next, take a drawing compass, insert a felt tip or other high visibility marker where the pencil normally goes; adjust the compass so that with the pointed end resting on the floor next to the LOWEST floor point, the marker rests against the bottom edge of the 2x4.

Holding the compass with the marker directly ABOVE the pointy end (trammel), drag the trammel point along the concrete maintaining contact between the marker end and the side of the 2x4.

What you should end up with, is a line along the 2x4 that is exactly parallel to your uneven floor; if you cut this line with a jigsaw and throw away the bottom part, , you should end up with a board whose irregular bottom edge should match your floor contour, and the top edge should be level.

Repeat this on both sides of the garage, they may be different.

Take a 5/8" masonry drill and drill holes through the existing slab every 3 feet or less along the outside of these "form" boards, and drive 2' long rebar pieces down thru the concrete until the top of the rebar is flush with the form board at each point along its length. This leveled "mini-slab" should extend under your outer walls (new sides) so your outer leaf will be level - standard J bolts can be added, as well as a thermal break such as sill seal, double 30# building felt - this is your outer leaf, so none of this will hurt isolation.

Perimeter Isolation Board would be laid against the inside of your outer wall frame, and the RIM rolled out in place - hell, you can read -

http://kineticsnoise.com/arch/pdf/rimc_install.pdf

'nuff said for now, I agree that 6" slab makes more sense in your case; when you talk to Dan, he may have the same questions about "overkill" as Jason did; I just explained that you wanted the ability to thrash drums at 3 am without your wife or neighbors finding more creative/disgusting/painful uses for your drumsticks... Steve
rod gervais
Senior Member
Posts: 1464
Joined: Wed Oct 08, 2003 1:48 am
Location: Central Village CT
Contact:

Post by rod gervais »

Shar,

Looking this over I have the following comments,

The direction you're heading is a pretty good choice,

The 6" slab is (IMHO) better not because of the additional isolation - but rather because of the lower center frequency (resonance) of the slab itself.

When you start talking islation in the area of 50+dB at 80hz, you are going to spend some serious money to match that with the remaining assemblies. But you would hate to have the slab create a problem due to it's resonant frequency.

Building Officials hate to see anything outside of their experience just sort of "pop up" - that's why they want to see details.

Of course - if one hires a licensed engineer to provide calcs and a stamped drawing - they will accept it as an "alternative design". But that get's fairly pricey.

As far as concerns with cracking goes, I have to say I am a bit nervous with the idea of pouring over the existing garage floor slab.

Personally I would remove it - then pour a thicker level slab with rebar reinforcement placed in the bottom 1/3 of the slab - before constructing my elevated slab.

Remember - this was not designed to carry this sort of a load - and you could have problems with cracking due to settlement, the chances are that the builder did not place any reinforcement in this slab - as typically that would not be require for a simple garage slab.

At most it might have some matting - but that never winds up being where it's supposed to be (which is in the top 1/3 of the slab - not the bottom - this for shrinkage control - not structural loading) but more probably only contains fibermesh in the concrete (once again for shrinkage (crack) control.

OK - that's my 2 cents worth.

Rod
Ignore the man behind the curtain........
sharward
Moderator
Posts: 4281
Joined: Mon Jan 03, 2005 4:08 pm
Location: Sacramento, Northern California, USA
Contact:

Post by sharward »

Here's a close-up of the area we're talking about...

<img src="http://home.surewest.net/sharward/studi ... -small.jpg">
(ENLARGE THIS PHOTO)
rod gervais wrote:. . . I am a bit nervous with the idea of pouring over the existing garage floor slab.
Thanks for weighing in, Rod (no pun intended!). Yes, I'm nervous about it too.
Personally I would remove it - then pour a thicker level slab with rebar reinforcement placed in the bottom 1/3 of the slab - before constructing my elevated slab.
WOW. :shock: This is beginning to take on a life of the "bunker project" in the UK!
Remember - this was not designed to carry this sort of a load - and you could have problems with cracking due to settlement, the chances are that the builder did not place any reinforcement in this slab - as typically that would not be require for a simple garage slab.

At most it might have some matting - but that never winds up being where it's supposed to be (which is in the top 1/3 of the slab - not the bottom - this for shrinkage control - not structural loading) but more probably only contains fibermesh in the concrete (once again for shrinkage (crack) control.
I just got off the phone with my builder buddy... He said he's almost certain that there's at least a 6" square thick wire mesh in the garage floor, and it may even have rebar in it. He said that my friendly neighborhood permit center would have the plans and that I could see and copy them there. I will try to do this tomorow morning.

So, let's assume for the sake of argument that my existing concrete floor will not handle the additional weight of the 6" floating slab + walls + ceiling. Let's assume it won't even handle a 4" floating slab + walls + ceiling.

M-A-M is heavy -- the greater the mass, the greater the weight. I'm wondering if I can "cheat" the laws of gravity by using an expensive product like QuietWood Solitude (4.4#/ft²) for my floor on top of the Kinetics Floating Wood Floor, and living with an unlevel floor in the room. The walls would still firmly attach to the walls, and the ceiling would still firmly attach to the walls.

I fully appreciate that conventional wisdom around here is that the QuietSolutions products are extremely expensive compared to what can be achieved with conventional products, careful design, and meticulous construction techniques (which is why we're all here). However, I'm between a rock (needing good iso) and a hard place (gravity, structural integrity).

I also realize that by going thinner, I'm looking at resonant frequencies and probably inferior low end TL... What I need to determine is whether my neighbors and I can live with those limitations -- and most importantly, whether I will be within the confines of my city's noise ordinances:I also know that although low end is harder to control, it is also generally harder for humans to hear... So perhaps I can get some clarification on that, perhaps in the context of this chart:

<img src="http://www.phys.unsw.edu.au/~jw/graphic ... Munson.gif">

In short, I need to know the numbers I must achieve, and whether or not my alternative QuietWood + Kinetics RIM will achieve them.

And once I have that, I'll redraw all my plans again. :?
Last edited by sharward on Mon Jun 20, 2005 5:09 am, edited 1 time in total.
knightfly
Senior Member
Posts: 6976
Joined: Sun Mar 16, 2003 11:11 am
Location: West Coast, USA

Post by knightfly »

I have the name/number of another Kinetics rep that handles the NW, will try Mon. or Tue. to see what he has to say on loading, etc... Steve
sharward
Moderator
Posts: 4281
Joined: Mon Jan 03, 2005 4:08 pm
Location: Sacramento, Northern California, USA
Contact:

Post by sharward »

Thanks so much for your followthrough, Steve. :mrgreen:
sharward
Moderator
Posts: 4281
Joined: Mon Jan 03, 2005 4:08 pm
Location: Sacramento, Northern California, USA
Contact:

Concrete Floor Details

Post by sharward »

Unconfirmed but believed to be reliable:

My existing garage concrete floor is 6" thick (and possibly up to 8" thick around the edges), and it is reinforced with rebar.

That is what the company has been doing for at least the past year for my builder.

I'm awaiting a callback from one of their managers who has been with the company longer and can hopefully confirm this.

If all of this is true, that's very encouraging -- right?
knightfly
Senior Member
Posts: 6976
Joined: Sun Mar 16, 2003 11:11 am
Location: West Coast, USA

Post by knightfly »

Yup - scenario #1 - you park a car that weighs 4000 lbs in that space; each tire has an approximate contact surface with the concrete of 6x8 inches, or 48 sq in. - each tire supports 1000 lbs, so at that particular location you have 20.8 PSI on the slab. Even a 4" slab won't break under those conditions.

Scenario #2 - you place an 11,000 pound slab on RIM's over your existing slab; if your particular RIM system has 2" square pucks on 24" centers, and your slab is 10 x 16, you would have that weight supported by a total of 4x6x9 sq in, or 216 sq in, for a psi rating of 11000/216, or 51 PSI.

Scenario #3 - same as #2 except pucks on 12" centers - now divide 11000 by (11x17x4), which gives 14.7 PSI.

Granted the total weight of slab is about 3x what a car weighs, so this will obviously not be "apples to apples", but with your thicker reinforced slab it should all be a moot point anyway.

I'll be finding out more about options with the Kinetics stuff in a couple of days... Steve
sharward
Moderator
Posts: 4281
Joined: Mon Jan 03, 2005 4:08 pm
Location: Sacramento, Northern California, USA
Contact:

Post by sharward »

Yeah, but that's just the weight of the slab -- there's also those pesky walls and ceiling to consider! :shock:

Any thoughts on using QuietWood Serenity atop Kinetics RIM Floating Wood Floor product? Totally inferior on low end TL? Any idea of the crazy-ass cost of that thing?
knightfly
Senior Member
Posts: 6976
Joined: Sun Mar 16, 2003 11:11 am
Location: West Coast, USA

Post by knightfly »

Yeah, stuff is somewhere around $200 a sheet IIRC - makes concrete look cheap by comparison, and concrete will blow its ass away (somebody should)

You want to drum, stick with concrete - whatever flooring you put on top of it, you NEED that mass... Steve