but it's only 160 CFM haha.You need 300. You have 560... Do the math.
That is certainly an option, but I will leave it as a last resort. I think I could make everything work knowing I can dump some air into my storage area.There's another option here: Just live with the higher flow rate! The "6 changes per hour" thing is the recommended rate, but if you don't mind a breezy room, you can have a higher rate... Roughly double, in your case. So as long as you then double the sizes of everything to keep the flow velocity at hte registers below 300 fpm, then that's fine.
Yes of course! I should have specified in my previous post. I figure I wouldn't need to add silencers for those ducts right? since it's a storage area.You would also need a return duct from that same storage room, back to the AHU. You need to think of this as a closed-loop system, except for the fresh air intake and stale air exhaust. The rest of the air recirculates through the AHU.
I'd rather not go this route since I can make use of the excess in better ways.You could also do a bypass on the system, with a duct that just loops the supply right back to the return, a little way upstream. Inefficient, and frowned on by many HVAC people, but possible. However, that's a lot of extra air to bypass!!
While this is an option for sure, I'd like to avoid this one as much as possible make use of what I have right now. I understand that the running costs might be a tad lower but probably not by much.Or you could sell that unit, and buy one half the size, which would have lower running costs, be quieter anyway, and would also provide the right amount of cooling and dehumidification.
Yes I did!! With 4-5 people rocking out with 3-4 amps in the room along with computer gear and lights, etc + latent heat load I estimate I'd need a max of roughly 32,000 BTU/hr.By the way, you DID calculate your sensible heat load and latent heat load completely, right? And you check that it matches the BTU capacity of the AHU fairly closely, right? What is the total load that you will be dealing with in your rooms, in BTU/hr?
Note that the AHU only has a heating coil currently and for the time being I will not be installing an A/C coil/system to my HVAC. At least not for the next couple of years. In fact we don't have central A/C for our 3500 sq/ft home....yet. Having a house shaded by the forest helps a lot...the max temp the house has seen in Celsius is roughly 26-27 degrees and I've lived there for 8 years now. I have used that room in the summer plenty as a work shop for years and while it does get warm in there it really isn't that bad. The studio/garage is on the north side of the house and doesn't see/get much direct sunlight.
While I totally understand it's not ideal, I do have a portable A/C unit that I plan on using on those special days and YES I do understand how those work and have a plan on how I can make that work when needed. There won't be much sound isolation if any when I use the A/C unit but that's something I can control. Whenever we decide to get central A/C I will be putting one in for the house and also one for the studio.
In terms of heating the studio in the winter, the AHU works really well. It's surprisingly really quiet doesn't take long before the entire room is warm. I currently keep the room at around 10 degrees when unoccupied and takes around 5-10 minutes for the room to heat up to 20 when I turn the heat on.
Question about the fresh-air/HRV requirements. @30% I'd need 92 CFM. Does this mean the branch ducts going to the HRV unit has to be sized on 92 CFM and most importantly do I add that to my total CFM requirements of the AHU? Just curious to know if that is totally separate from AHU.
I know that HRV units have their own fans.
Francis,