Help with one room studio design in Delta BC, Canada

Plans and things, layout, style, where do I put my near-fields etc.

Moderators: Aaronw, kendale, John Sayers

Bhudie
Posts: 20
Joined: Sat Jan 31, 2015 8:28 am
Location: Delta, BC Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Bhudie »

OK Greg... you got me. Just when I thought I had things under control you ask some questions that remind me how much I don't really know... :)

Let me give this a try... but I think I'll have more questions then answers again...
Are you doing forced air or a ductless minisplit?
Well... I guess I would say forced air. But now I'm not sure...
I have radiant floor heating built in to the concrete so my main concern was getting fresh air into the room to not kill myself, and secondary concern was A/C for the hotter months. That's why the first time I answered that I was just thinking of adding a fan at the supply of my ducting to pump the appropriate amount of fresh air into the room. Naively I was thinking that I could then down the line (maybe after the setback inspection) change the fan out with something like a heat pump to control the A/C in the hotter months and still provide the necessary fresh air.

However, you then rightly pointed out that I'd be dumping cold air onto my feet in the winter with my current plan and I started looking into the heat pump/HRV systems. My understand now is that the heat pump sometimes will cut off the fresh air completely depending on the external temperature and what it's trying to do (heat or cool), so this might not actually be a viable plan. But I must admit though, that after trying to research a bit I am not confident that that statement is necessarily correct, and I think I'm more confused now than before about how all these systems work (HRV/Heat Pump/AC unit etc.) and on what I should be doing with my plan. :oops:

I'm assuming that you pointed this out:
1. I don't see a designated air handler in your space.
2. Due to your back wall architectural guidelines, there is no room for your returns to get back to an ducted air handler.
Because through my research the heat pump also utilizes the air from the exhaust too, thus the need to pipe back to the air handler?
Therefore, I'm guessing that you're using a ductless mini split?
Well... I wasn't... but to be honest, now I feel like I really don't know what I am doing and a bit back at square 1... well, maybe square 2 or 3, but either way a whole lot more figuring to do.
If so, you could get away with WAY less cross sectional area than you're currently calculating. This means smaller silencer boxes.

Okay so, if you have 1240 cubic feet, yes 6 air changes is 124 CFM. Now, that's needed if you're rocking a ducted system. For fresh air, which your silencer boxes are passing, you only need ~ 30% of that amount. So, 124CFM x 30% = 37.2 CFM. Much less, right? You might have troubles finding an inline fan that will move only that amount of air. You might have to get crafty. Also, before I forget, I need to point out that due to your current design, you can't fit an HRV in there which as I'm sure you know would be really really smart to have in BC climate. If are aren't cool dumping all of your conditioned (heated) air out into the cold winter and then have your fan blowing really cold air in on your feet (under your speakers), you certainly should consider an HRV unit.

Anyway, the smallest round duct you're going to find around your area might be 5" flex duct. Unfortunately, this crap isn't duct LINED, it's insulated. So, we have to rely on the low frequency attenuation in any flex duct runs and rely on the silencer boxes for the mid/high frequency attenuation.

5” RD duct = 19.63 sq in. Double = 39.26 sq in.

That means that the inside total cross sectional area of your silencers only need to be 39.26 sq in. in order to achieve doubling of your cross sectional area. You wrote that each silencer box in your joists has a cross sectional area of 36". So you're ~91% there with a SINGLE joist cavity of boxes! Let's say you have two joist cavities of boxes. That gives you 72 sq in. Now, going from 5" inlets on the box to 72 sq in inside, you've increased your area by 3.67 times! Now THAT's an impedance mismatch. Kick ass. Also, regarding velocity:

Air velocity in ft/min = CFM Flow rate in ( ft3/min) / CSA Cross sectional area in ft2
Air velocity in ft/min = 37.2 CFM / 72 sq in
Air velocity in ft/min = 37.2 CFM / 0.5 ft2
Air velocity in ft/min = 74.4 feet per minute. Now THAT is slow :yahoo:
This all sounds fantastic save for the dumping cold air on the feet part, but as I said before, I am now back to trying to figure out what system I really do need so I can figure out if this is indeed applicable to me.
1. show us where you're putting the mini split.
2. you should have your fresh air blowing in right ABOVE your indoor mini split head unit, not the floor under your speakers.
3. try to implement an HRV into your design and put it in the pool mechanical room (I have one really bizarre idea of how to get your duct work on your ceiling joist boxes into the pool room)
3b. since it's a mechanical type room, I'm guessing there's a floor drain in there you could use as a drain for your mini split yeah?
If this is the way I go I will do all of these things. But given what you know now from my requirements (no need for heat, mostly fresh air, secondarily cooling, but given my climate only in a couple months in the summer...) is this the system you would suggest? I also have a bit of tissue rejection from the actual unit that is mounted in the room for the mini-split since it's big and ugly... but if it's what I need I could get over that...
4. you're making insanely good progress here so please stay with us and as you can imagine, once this HVAC crap is behind you, you'll be off to the races!
Thanks for the positive encouragement... although it feels more like I just took a punch to the gut :lol:
But sincerely, thank you for all the help, I wouldn't have gotten this far without you and Stuart... and I will press on, and hopefully this is just a small set back in my planning process.

Apologies for my ignorance...

Thanks,
Aaron
Gregwor
Moderator
Posts: 1501
Joined: Wed Feb 01, 2017 6:03 pm
Location: St. Albert, Alberta, Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Gregwor »

Well... I guess I would say forced air. But now I'm not sure...
Forced air means either a heat pump that drives a coil/fan unit the size of a small furnace that then blows air through ducts of your original calculation size. It needs supply duct work FROM the fan unit and return air BACK to the unit, just like a normal furnace runs here in Western Canada. Then, you need fresh air from outside and stale air pumped outside just like our homes here have. In Western Canada, HRV's are standard in new builds and as far as I know even required here in the Edmonton area. As I described in my last post, it doesn't make sense to blow all of your heat outside only to replace it with -20 cold air. HRV's are quite efficient. So yeah, with a ducted system, you have a lot of duct work required

If you go with a ductless mini split, sure you'll have a big, kind of ugly looking unit on your wall, but it will do all of your cooling and heating, taking over where your floor fails to keep your room nice and warm when you aren't in there during the brutal cold month of February. Also, it will keep the air nice and comfortable during super hot summer months when you and your friends are hanging out working on tunes in your room. The duct work I described in my last post can be nice and small and literally just replaces your stale air with nice fresh air from outside. Running it through an HRV will save you a ton on heating/cooling costs and also keep the air being brought in from outside at almost the same temperature as the air in your room! Your biggest issue may be finding a small single room HRV as most run around and above 100 CFM. I know small ones exist, but I couldn't link you to one right now.

You'll also need to find out where you can put the heat pump for your mini split. Luckily, they are small and really quite quiet outdoor units.
Because through my research the heat pump also utilizes the air from the exhaust too, thus the need to pipe back to the air handler?
In a ducted system, yes. As I described above, it runs just like a regular Western Canada furnace does.
is this the system you would suggest?
For what you're doing, yes. Just make sure you get a low temperature good brand name (like Mitsubishi or at worst case, get a Fujitsu) mini split. You'll see that if you get a cheap one (even if it's a good brand), they don't operate at low temperatures like we get in our area. The low temp ones only heat EFFICIENTLY down to like -25 celcius which is probably fine for you. It's a bit colder here in Alberta. It'll still throw heat below that temperature, just not as efficiently. Plus, your in floor heating will help keep you warm in those cold times. If you ever feel the need to have your mini split throw max heat at very low temperatures, you can add on modules to the unit.
Thanks for the positive encouragement... although it feels more like I just took a punch to the gut :lol:
But sincerely, thank you for all the help, I wouldn't have gotten this far without you and Stuart... and I will press on, and hopefully this is just a small set back in my planning process.
You're doing awesome man! I hope you feel confident that you're doing the right thing. Think of all of the people who just throw rooms up with zero knowledge of studio design. Your place is going to rule and you can be so proud of it. Thank you for being part of the forum!
Apologies for my ignorance...
Don't apologize! I was in your shoes not to long ago and I have to tell you, learning about this stuff is so cool. And it's so awesome to help people out answering questions that you've learned the answers to the hard way! Having said that, I truly feel the best way to learn this stuff is to read threads regularly and try to help people out. It forces you to do research on topics you don't know well and most of the time, you then learn things that directly apply to your own build. Before you know it, you can answer most of the questions without looking anything up! So please feel free to chime in and answer peoples questions on here. If we all help one another out, it makes for a better forum and better studios all over the world!

Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
Bhudie
Posts: 20
Joined: Sat Jan 31, 2015 8:28 am
Location: Delta, BC Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Bhudie »

Thanks again for all your help Greg.

Still trying to wrap my head around this... I think the mini-split is the way to go.

I am trying to figure out where the best place to put it is, I'm guessing that maybe front centre up high on my baffle wall might be a good place, because I could at least partially hide it with the cloud. I can also still pipe fresh air in just above it just like my previous plan had. I've asked my contractor if mounting the heat pump for the mini-split on the ground on that east wall is going to be a problem for setbacks, and am waiting to hear back.
The duct work I described in my last post can be nice and small and literally just replaces your stale air with nice fresh air from outside. Running it through an HRV will save you a ton on heating/cooling costs and also keep the air being brought in from outside at almost the same temperature as the air in your room!


Question for you though:

1) Do I still need to run my exhaust air back to the supply to put an HRV in line with my fresh air supply? Or does the HRV just draw air from the outside?


My thinking is that if my fresh air requirements are less, then the 2 big supply silencers will get smaller and I could put the HRV in the pool equipment room. (Caveat that this is all before I've done my HRV research so I'm hoping that this is possible... going to do research now...)

Thanks,
Aaron
Soundman2020
Site Admin
Posts: 11938
Joined: Thu Aug 21, 2008 10:17 am
Location: Santiago, Chile
Contact:

Re: Help with one room studio design in Delta BC, Canada

Post by Soundman2020 »

1) Do I still need to run my exhaust air back to the supply to put an HRV in line with my fresh air supply? Or does the HRV just draw air from the outside?
An HRV does what it says: it Recovers the Heat in the Ventilation air: It extracts the heat that is in one flow of air going one way, and transfers that heat to the other flow of air going the other way. So it MUST have both a supply duct AND an exhaust duct: it has the transfer he heat FROM one of those TO the other one. If you only have one stream, then there's nothing to transfer from/to.

So which way does it transfer? Heat always flows from hotter to colder, so whichever stream is hotter will end up cooler, and whichever stream is cooler will get warmer. Which is very fortunate for us, because in summer, when your HVAC system is cooling the room, the cool room air that you are sending out through the exhaust will be heated up from the heat in the incoming air from outside, and that incoming air will therefore end up cooler. In effect, the HRV will seem to have transferred the "cold" from the outgoing air to the incoming air, and relatively speaking, that's true.... But in absolute terms, the heat went from the incoming hot air to the outgoing cold air.

Then in winter, when your HVAC system is heating the room, it works the other way around: the outgoing hot air will have it's heat transferred to the incoming cold air, which is exactly what you want.

So in both summer and winter, the heat is transferred the way you want it to be. As Greg mentioned, these units are quite efficient and can recover a very large percentage of the heat, saving you big money on heating and cooling bills.

There's another type of system, called an "ERV" for "Energy Recovery Ventilator", and it does even more: it also transfers humidity, which recovers even more energy... but it's more complex, and only works in climates where there's going to be a big difference in humidity between the indoor air and outdoor air. If the humidity is similar, only differing in a few percentage points, then it won't be able to move that humidity very well.
I could put the HRV in the pool equipment room.
You can put it wherever you want, basically, provided that the ducts are suitably insulated if it is in a very hot or cold location, and/or if it is far from the room (long ducts). And here to, you have to be careful with static pressure: like any other fan, the HRV can only deal with a certain maximum static pressure, so do make sure that you design your duct system with that in mind.


- Stuart -
Gregwor
Moderator
Posts: 1501
Joined: Wed Feb 01, 2017 6:03 pm
Location: St. Albert, Alberta, Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Gregwor »

How HRV Works.jpg
Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
Bhudie
Posts: 20
Joined: Sat Jan 31, 2015 8:28 am
Location: Delta, BC Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Bhudie »

OK. Here's what I'm thinking now. Caveat that it might not work because I am not sure that I can get the flex duct to the pool room, and that I need to go to the site to look at a few things to see if it's plausible... but here's where I am thinking.

- CFM of fresh air requirement = 37.2 CFM
- 2 runs of silencers on inner leaf with ~72 sq inches of cross sectional area total
- Connected to 2 runs of 5" diameter flex duct (total cross sectional area of 19.6x2=39.2 square inches), that joins together to 1 run of 5" diameter flex duct (cross sectional area of 19.6 square inches) and runs 90 degrees to the pool equipment room.
- That flex duct then connects to my outer leaf Silencer on the inside of the outer leaf in the pool equipment pop out outer leaf wall, with a cross sectional area of 60 sq ins for a 3x impedance mismatch.
- Outer leaf then connects to HRV in the pool equipment room, which then connects back to the outer leaf silencer on the inside of the outer leaf for the supply. Same size cross section as return outer leaf silencer.
- which connects to the inner leaf silencer in the same box out with the same cross sectional area.
- which then is ducted to vent above a mini-split near the top of the centre of my infinite baffle.
- Mini-Split goes out the east wall to the heat pump mounted on the ground. (not modeled yet in Sketch Up.)

Looking like this:
LatestAttemptWithHRVResized.jpg
LatestAttemptWithHRV_TopViewPoolEquipRoomResized.jpg
LatestAttemptWithHRV_CloseUpPoolEquipRoomResized.jpg
Things I need to figure out:
- if I can find an HRV that blows as low as 37.2 CFM, and can handle the static pressure of the system. (will do some research on this one tonight.)
- if I can find a path for the 5" flex duct to the pool equipment room. (dicey, but I'm going to the site now to check this out)
- Contractor to confirm that I can put the mini-split heat pump on the ground and not violate the setbacks.
- Have to source an economical mini-split that fits my purposes.
- Need to appropriately size registers for another impedance mismatch... but should be easy to do this given the lower CFM.

One question:

1) How does one do the calculations to figure out the static pressure of the system? I know I'll need to take this into account for the HRV requirements...



I feel like this can work if I can figure out the ducting, but I wouldn't mind a sanity check from you Greg, or Stuart.

And as always... thanks for all the help.

-Aaron
Soundman2020
Site Admin
Posts: 11938
Joined: Thu Aug 21, 2008 10:17 am
Location: Santiago, Chile
Contact:

Re: Help with one room studio design in Delta BC, Canada

Post by Soundman2020 »

- Mini-Split goes out the east wall to the heat pump mounted on the ground. (not modeled yet in Sketch Up.)
If you can't put it there, then it's probably not a problem. The system likely comes with tubing that is several meters long, and it is possible to buy extension kits to get several more meters out of that. Check the manual for the systems you are thinking of BEFORE buying to see what the limit is. In the specifications section, or the installation section, it should tell you what the maximum allowed tubing length is.

Caveat: Don't buy ordinary copper water pipe and try to make your own extensions! Won't work. Buy the correct complete kit, with the connectors already attached on both ends. The type of pipe used in HVAC systems is specially meant to carry the very high pressure gasses and liquids. Normal copper pipe is no good for that. Also, you cannot solder HVAC pipes with ordinary electronic solder and a soldering iron: you need special silver solder and very high temperatures to solder HVAC pipe. In fact, it isn't really soldering at all: it is brazing. Not worth learning to do that yourself. Just buy the correct pipe kit for the length you need, then hire a qualified HVAC installer to connect it all up for you, and charge the system with gas... not something you should try to do yourself! You can probably mount the compressor and indoor unit yourself, and also cut the holes and push the pipes/wiring through, but don't try to do the connection of those pipes. Don't even take off the protective caps!

Also, it's a minor but still important point but part of the "bundle" of pipes, tubes and wires that connect the indoor unit (sometimes called the "condenser") to the out door unit (usually called the "compressor" or sometimes the "heat pump"), is the condensate drain pipe. It drains away the water that will condense on the cooling coils of the indoor unit, from the humidity in the air. That pipe must always descend, never climb. It must always slope downwards, all the way from the indoor unit to wherever you want the water to go. Sometimes, that takes careful planning. What moves the water through that pipe, is just gravity. Water can't climb uphill... it always flows down. Thus, no part of the pipe must ever be higher than the bottom of the indoor unit, or the water will never run down the pipe: it will accumulate in the drip pan inside the unit, then overflow and run down your wall... So do take that into account. That condensate drain pipe is usually a flexible plastic pipe, and it does not actually need to go to the compressor: you can guide it anywhere you want to let the water drain out. So it doesn't need to follow the same path as the rest of the "bundle", and it can be as long as it needs to be to get wherever it is going... provided that it always slopes down.

- Stuart -
Gregwor
Moderator
Posts: 1501
Joined: Wed Feb 01, 2017 6:03 pm
Location: St. Albert, Alberta, Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Gregwor »

- Connected to 2 runs of 5" diameter flex duct (total cross sectional area of 19.6x2=39.2 square inches), that joins together to 1 run of 5" diameter flex duct (cross sectional area of 19.6 square inches) and runs 90 degrees to the pool equipment room.
The only downside to this plan of attack is that it prevents you from building your ceiling inside out. What if you built inside out all the way to the front of your room at which point you left one joist traditional in order to run your duct down it as it is in your current drawing. You'd just have to rearrange your pool room silencer boxes to accommodate this configuration. You REALLY should build inside out to maximize your room volume.
- That flex duct then connects to my outer leaf Silencer on the inside of the outer leaf in the pool equipment pop out outer leaf wall, with a cross sectional area of 60 sq ins for a 3x impedance mismatch.
The penetration of your outer leaf wall going into your pool equipment room NEEDS to be the sleeve of the silencer box. You have it drawn that the flex duct penetrates the wall. But think about it, the flex duct is very thin and light and the mass of your outer leaf is not maintained. The sound can just blow right through the light plastic duct sleeve. If your 1" MDF silencer sleeve is going through the leaf instead, with caulk around it, the mass is maintained and attenuated through the silencer box so it's nice and quiet by the time it exits the silencer!
- Outer leaf then connects to HRV in the pool equipment room,
HRV's have filters in them that need to be cleaned. The Fantech model in my house has a lid that unclips so it can lift out of the way. This would work in your current design, but I'm just suggesting that you make sure whatever model you buy can be accessed in the little space you have the HRV housed in.
- if I can find a path for the 5" flex duct to the pool equipment room. (dicey, but I'm going to the site now to check this out)
There is ALWAYS a way!
- Need to appropriately size registers for another impedance mismatch... but should be easy to do this given the lower CFM.
Don't worry about impedance mismatch here. By nature it has a HUGE impedance mismatch! It's going from your small silencer cross sectional area to the entire volume of your room! What you need to worry about is air velocity and what the NC rating of your registers are. Also, regarding registers, make sure they throw the right direction. They're expensive, but check out Nailor brand stuff as they have great documentation on their products.
1) How does one do the calculations to figure out the static pressure of the system? I know I'll need to take this into account for the HRV requirements...
I posted my static pressure calculation spreadsheet on this page (7th post from the top):

http://www.johnlsayers.com/phpBB2/viewt ... =1&t=21752

It's very annoying to do.
And as always... thanks for all the help.
As always Aaron, your hard work is evident.

Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
Bhudie
Posts: 20
Joined: Sat Jan 31, 2015 8:28 am
Location: Delta, BC Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Bhudie »

If you can't put it there, then it's probably not a problem. The system likely comes with tubing that is several meters long, and it is possible to buy extension kits to get several more meters out of that.
Good to know, Stuart. Thanks for that, and all the detail about tubing as well!
The only downside to this plan of attack is that it prevents you from building your ceiling inside out. What if you built inside out all the way to the front of your room at which point you left one joist traditional in order to run your duct down it as it is in your current drawing. You'd just have to rearrange your pool room silencer boxes to accommodate this configuration.

OK. I'll look into this.
The penetration of your outer leaf wall going into your pool equipment room NEEDS to be the sleeve of the silencer box. You have it drawn that the flex duct penetrates the wall.
yeah, I had intended for it to be a sleeve, I just mocked up the drawing quickly to show the concept. I am working on details now...

Which brings me to a couple of questions I have:


1) What's the best way to connect a rectangular sleeve to round flex duct, and still maintain a seal?

2) I'm thinking whatever the answer to number 1 is will also apply to connecting the end of my inner leaf silencer box to round flex duct as well, but in the event it doesn't, what's a good way to do that too?


HRV's have filters in them that need to be cleaned. The Fantech model in my house has a lid that unclips so it can lift out of the way. This would work in your current design, but I'm just suggesting that you make sure whatever model you buy can be accessed in the little space you have the HRV housed in.
Good call, and will do.
They're expensive, but check out Nailor brand stuff as they have great documentation on their products.
Thanks for the tip!
I posted my static pressure calculation spreadsheet on this page (7th post from the top):

viewtopic.php?f=1&t=21752

It's very annoying to do.
Took a quick scan, haven't gotten into it fully yet. But again, thanks for the link!

-Aaron
Gregwor
Moderator
Posts: 1501
Joined: Wed Feb 01, 2017 6:03 pm
Location: St. Albert, Alberta, Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Gregwor »

1) What's the best way to connect a rectangular sleeve to round flex duct, and still maintain a seal?

2) I'm thinking whatever the answer to number 1 is will also apply to connecting the end of my inner leaf silencer box to round flex duct as well, but in the event it doesn't, what's a good way to do that too?
To obtain the impedance mismatch, try to avoid smooth conical type transitions. Just fix one of these to your box (apply caulk to the bottom side of the ring before you brad nail it on), seal the hell out of it with mastic and you're good to go!
Ductboard Take Offs.png
Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
Bhudie
Posts: 20
Joined: Sat Jan 31, 2015 8:28 am
Location: Delta, BC Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Bhudie »

Hey Guys,

I have a random selection of a few more questions for you.

1) Is there any reason why an inside out ceiling wouldn't work with joists that are 16"OC? I think I read somewhere Stuart suggesting that he normally sisters the joists at 24"OC with blocking every 48". With 16"OC I'm assuming my ceiling panels would be more plentiful and long and skinny, but maybe still doable...

2) And also is there anything I should consider with respect to the inside out ceiling if I'm doing conventional walls (non-inside out)? My inner leaf ceiling joists are hung from the walls, not built on top. I'm assuming as long as the top plates of the walls are acoustically sealed where they meet the ceiling panels I would be ok, true?

3) If I can do inside out ceiling, am I right to think that I could run the electrical wiring through the joists just below my ceiling panels to my track lights to preserve the one entry into the room? This way I could cover that wiring with acoustic treatment after the fact.

4) If I do inside out, and fill the ceiling cavities with treatment, am I running the risk of making the room too dead with 2-4" worth of 703 or similar?

5) For my cloud above my listening position, I haven't yet had the chance to properly do my vertical plane ray tracing, but I believe I read Stuart somewhere recommend pulling the cloud away from the baffle wall, as the reflections right up against the baffle wall aren't going to reflect to my listening position. I imagine that it's pretty unique per room, but is there a rough guideline on how far away from the baffle the cloud could be? I'm pretty sure the answer is I need to do the calculations/Ray-Tracing, but I was thinking I might put a track light between my cloud and my baffle wall if there would be enough room, so I am just trying to understand roughly if that is going to be a bad idea or not...

Sorry for the shotgun questions without much context from my side, but my electrician is on site tomorrow and I want to discuss where the lighting should be going with him... I was hoping to have had time to finish my design by now so I would know exactly where to tell him but life has gotten in the way :( .

I figure if I can wrap my head around the possibilities a bit better, then I could buy myself the time to finish the design properly.

Thanks again,
Aaron
Gregwor
Moderator
Posts: 1501
Joined: Wed Feb 01, 2017 6:03 pm
Location: St. Albert, Alberta, Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Gregwor »

1) Is there any reason why an inside out ceiling wouldn't work with joists that are 16"OC? I think I read somewhere Stuart suggesting that he normally sisters the joists at 24"OC with blocking every 48". With 16"OC I'm assuming my ceiling panels would be more plentiful and long and skinny, but maybe still doable...
The larger the distance between joists the better. This is because the sheathing can then flex more. If you look at any tests done, 24 OC is better than 16 OC.

Ultimately, you need to get an engineers stamp saying your ceiling design will hold the load you're putting on it. You could probably have greater OC distance using LVL studs (West Fraser is manufactured near you -- that's what I got) but 2x8's (which is 7 1/4" deep) is as small as they come. To run ~22' my engineer had me sister these and that got me 25.5" OC. For my smaller room I didn't have to sister.
2) And also is there anything I should consider with respect to the inside out ceiling if I'm doing conventional walls (non-inside out)? My inner leaf ceiling joists are hung from the walls, not built on top. I'm assuming as long as the top plates of the walls are acoustically sealed where they meet the ceiling panels I would be ok, true?
You CANNOT hang your ceiling joists from the walls. Your walls need to be built shorter so that the joists can rest on top of the double top plates. Your contractor will know this. You need to install a sort of rim board (just use regular 2x8's of whatever dimension your engineered joists are). Then you lift your modules into place. Your perimeter modules can rest on top of the walls. I recommend building the perimeter modules first and then build custom sized ones to slip up into the middle. This will allow all of your perimeter modules to rest on top of the walls.

The other thing you need to consider is vapour barrier. Remember, it must be snug against the COLD side of your inner leaf sheathing.
3) If I can do inside out ceiling, am I right to think that I could run the electrical wiring through the joists just below my ceiling panels to my track lights to preserve the one entry into the room? This way I could cover that wiring with acoustic treatment after the fact.
Correct. All of your wiring can run up inside of the frame work hidden by your insulation/fabric.
4) If I do inside out, and fill the ceiling cavities with treatment, am I running the risk of making the room too dead with 2-4" worth of 703 or similar?
Possibly, but that's where you can tune your acoustic response with things like plastic, wood slats, etc depending on how your room shapes up acoustically speaking. In a control room it's typical for the entire ceiling to be filled with insulation. As long as you don't put fabric over it during your treatment stage, it's easy enough to tune it as I've described and THEN cover it up with fabric.
5) For my cloud above my listening position, I haven't yet had the chance to properly do my vertical plane ray tracing, but I believe I read Stuart somewhere recommend pulling the cloud away from the baffle wall, as the reflections right up against the baffle wall aren't going to reflect to my listening position. I imagine that it's pretty unique per room, but is there a rough guideline on how far away from the baffle the cloud could be? I'm pretty sure the answer is I need to do the calculations/Ray-Tracing, but I was thinking I might put a track light between my cloud and my baffle wall if there would be enough room, so I am just trying to understand roughly if that is going to be a bad idea or not...
Your electrician can't really run anything because your room isn't built yet. But yes, plan for a lighting circuit in your cloud area. You will have to ray trace it to see how much space you'll have along the front of your cloud. You might only be able to put some strip lighting there. Or heck, maybe your design will end up not having any lights there. Either way, plan to run wires there.
Sorry for the shotgun questions without much context from my side, but my electrician is on site tomorrow and I want to discuss where the lighting should be going with him... I was hoping to have had time to finish my design by now so I would know exactly where to tell him but life has gotten in the way :( .

I figure if I can wrap my head around the possibilities a bit better, then I could buy myself the time to finish the design properly.
I've been swamped so I apologize if I haven't been super quick to respond. As you can see, the design stage is the most important. It's not worth rushing anything. You've made great and fast progress. Keep it up!

Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
Bhudie
Posts: 20
Joined: Sat Jan 31, 2015 8:28 am
Location: Delta, BC Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Bhudie »

Hey Greg,

Thanks again for all the help. I feel like I have a plan that works now for the HVAC... met with the contractor and found a way to run the 5" Flex duct to the pool equipment room, so now the only thing I still need to do is find an HRV that can go as low as 37.5CFM. Will get on that next.
The larger the distance between joists the better. This is because the sheathing can then flex more. If you look at any tests done, 24 OC is better than 16 OC.
Got it. Thanks!
The other thing you need to consider is vapour barrier. Remember, it must be snug against the COLD side of your inner leaf sheathing.
Is there an acoustical/isolation effect of this? or are you just speaking on the correct place to put it in terms of code/construction?
Possibly, but that's where you can tune your acoustic response with things like plastic, wood slats, etc depending on how your room shapes up acoustically speaking. In a control room it's typical for the entire ceiling to be filled with insulation. As long as you don't put fabric over it during your treatment stage, it's easy enough to tune it as I've described and THEN cover it up with fabric.
Got it. Thanks!
You will have to ray trace it to see how much space you'll have along the front of your cloud.
OK... I took a stab at this, but I'm a bit confused about where to vertically ray trace from. I'm assuming that I do it from each speaker, and not the front centre of my baffle wall.

Trying to do this I struggled to do it in 3D in Sketchup so I made a 2D version of the vertical space on the side and came up with this:
VerticalRaytraceFromBaffleWall.jpg
I was able to clear 2.5' either side of the centre of my head with a 4' long cloud at a 25 degree angle sloping away from the baffle wall...

However, when trying to convert this to 3D space, I basically just mirrored the same cloud above the other speaker and got sort of a weird peaked convex shape. I am worried that this method isn't the right way to do this.
SlightlyPeakedCloud.jpg
Here's another angle from a bit higher up so you can see the peak...
SlightlyPeakedCloudShowingPeak.jpg
Also, I'm not sure how I ray trace from the other speaker in the vertical plane given this model, as it starts to present some weird angles. I thought I'd check in to see if there is better approach to this.
I've been swamped so I apologize if I haven't been super quick to respond.
Are you kidding me? Both you and Stuart have been amazing. I don't think I could have gotten this far without you.

Thanks again,
Aaron
Gregwor
Moderator
Posts: 1501
Joined: Wed Feb 01, 2017 6:03 pm
Location: St. Albert, Alberta, Canada

Re: Help with one room studio design in Delta BC, Canada

Post by Gregwor »

Is there an acoustical/isolation effect of this? or are you just speaking on the correct place to put it in terms of code/construction?
Purely for code and to prevent moisture/rot issues from happening!
Trying to do this I struggled to do it in 3D in Sketchup so I made a 2D version of the vertical space on the side and came up with this:
I do it from the acoustic axis center line of the speakers similar to what you're doing too.
However, when trying to convert this to 3D space, I basically just mirrored the same cloud above the other speaker and got sort of a weird peaked convex shape. I am worried that this method isn't the right way to do this.
That's a pretty cool look but convex shapes are not good acoustically and that would also be very hard to build accurately. Typically what happens after the ray trace is that you just build the cloud straight across the room.
Also, I'm not sure how I ray trace from the other speaker in the vertical plane given this model, as it starts to present some weird angles. I thought I'd check in to see if there is better approach to this.
Draw your cloud straight just like all of the clouds you see on the forum and double check that your RFZ sphere around your head is maintained.

Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
Purelythemusic
Posts: 56
Joined: Wed May 30, 2018 7:31 am
Location: England, Bristol
Contact:

Re: Help with one room studio design in Delta BC, Canada

Post by Purelythemusic »

This is such a useful thread to follow, thanks for keeping up the work and detail!

Yes the Vapour membrane as Gregwor has said is very important, in the uk you are able to use fairly thin plastic sheet but we normally use the same stuff we use for Damp membranes... slightly thick at corners when folding but you don’t want vapour problems...

I’m not sure if this has been covered but do mini splits typically control humidity at adjustable levels or do you need to get certain models that can do it? I should probably google!

Tom