I will use a split a/c unit for heating and cooling.
The ventilation will be separated from the a/c.
So your ventilation ducts only need to provide you with 25-30% of your required CFM provided by your split unit. Have you calculated your required CFM yet? What about your heat gain, heat loss, sensible heat and latent heat? Without knowing these values, there's no way to know what unit to buy.
I will try to find the spreadsheets, if by any chance you have a link please share it
Sounds like you found one. If you for some reason can't make yours work, I can PM you mine.
I will try to do that. You see being a father of two boys, 2 and 3 years old, and working two jobs leaves you with almost no free time..but I will try my best!
I feel your pain. I have a boy who is almost 4 and a daughter turning 2 on Friday! I also have 5 jobs and no child care. My studies usually happen when everyone else is asleep, when I'm on the toilet - taking extra long of course

, or I have just not worked as I need to prioritize my acoustic studies and designing.
In the meantime This is the design of the silencer:
(still working on the dimensions though)
Looks like a standard silencer. Once you calculate your static pressure, you can determine if you can shrink the straight run parts of the design as that will increase the static pressure, but will provide you with more impedance mismatches. Where you want to make sure you have large cross sectional areas is at the corners as small cross sectional areas at corners will introduce a lot of static pressure. Increasing the cross sectional area at the corners will again provide you with more impedance mismatches (this is a good thing).
Ok I found some spreadsheets over the net for calculating the static pressure etc.
It really seems impossible for me to do the calculations, I don't even know where to start
And I can't really afford to hire someone to do it for me..
You have to find the time to research this and learn it. Here is some info:
BTU = British Thermal Units = the quantity of heat required to raise the temp of one pound of water one degree Fahrenheit
Static Pressure is in Pa units. Your Air Hander Unit must be able to handle more Pa than the system is
Design cooling load (or heat gain) is the amount of heat energy to be removed from a house by the HVAC equipment to maintain the house at indoor design temperature when worst case outdoor design temperature is being experience.
Two types cooling loads:
- sensible cooling load = the dry bulb temp of the building (this is basically the air temperature we feel)
- latent cooling load = the wet bulb temp of the building (this is basically moisture from things like us sweating)
Heat gain = heat from components within or on a building such as people, appliances, sunlight, etc.
Heat loss = heat leaves through crack, windows, etc and cold air comes in
Sensible heat = actual temperature --> amount of energy needed to increase or decrease the temp of some substance
Latent heat = basically, humidity --> heat that results from an increase or decrease in the amount of moisture held by the air. The amount of energy needed to cause a phase change (liquid to gas, or gas to liquid) without changing the actual temperature of a substance.
For your calculator, all you really need to do is enter how many feet of each type of duct work there is. But, as you can imagine, you pretty much have to 3D model the entire system to know how big things are and how long they are.
so I think I will just stick to the current plan
-making the silencers twice bigger than the duct size,
-two silencer for each path-one inside the room and another one outside- (total of four) for in and out air
-use rigid round ducts where needed,
-frame paths with double drywall or OSB for the extension boxes,
-double OSB for the silencers,
-2'' duct line
and hopefully will work..
"hopefully"
I 've been reading here that the point of the registers should be twice the cross sectional area and with a cone type register so will not introduce any sudden changes.
I don't want to say "no". But to make my point, I'll say no, even though that's not an entirely wrong statement.
So, the registers have to be "large" enough to provide you with an air velocity of less than 300 feet per minute. Ideally, you want it even slower than that, but for most recording situations, 300 will provide you with a low enough noise floor to be acceptable. If your velocity is faster than this, recordings of acoustic guitar or soft singing with compression applied could result in the wind noise most high velocity home HVAC systems have. I think we've all watched YouTube videos with horrible background noise. That's typically from noisy HVAC.
Your air velocity can easily be calculated by:
Air velocity in feet per minute = CFM divided by your cross sectional area
So, once you know your CFM which is also a simple calculation of:
CFM = [(# of air changes per hour... which is typically a minimum of 6) multiplied by the volume of your room in cubic feet] divided by 60 minutes
And we already know the air velocity has to be <300 feet per min
Again, so once you know your CFM, you can do some basic algebra and rearrange the first equation to be:
Cross sectional area = CFM/air velocity
so
CSA = CFM/300
That will give you the MINIMUM CSA your register can be. Make it a bit bigger to play it safe.
To comment on the last section of your comment regarding the cone shape to not introduce sudden changes. Well, it's true that a gradual change in CSA like a cone (or wave guide) provides will prevent distortion or turbulence, the true rule of thumb is that you need a certain distance between any direction change or CSA change and the mouth of your grille/register. I've heard two values for this distance. It's either 3 or 5 times the diameter of that which is feeding the grille/register. So let's say your have a 4" round duct that goes to a required 6" round grille, you'd need a distance of between 12 and 20" of straight duct to prevent noise at the mouth.
Having said that, in my case after the silencer which will be at the back of the room I will use rigid duct to travel at the front of the room so that the fresh and the old air are far away from each other, to create a kind of flow.
The duct will have half the cross sectional area of the silencer and as you told me that's not a problem.
You will get higher insertion loss with smaller duct as the ratio of CSA to insulation is greater. That is all. I did not mean to imply that small high velocity duct is not a problem specifically with your design. It may introduce too much static pressure. Until you calculate it, you won't know. Realize that with too much static pressure, your fan will stall and you will get no ventilation. Or best case scenario, you will burn out your fan motor.
But if I indeed have to make the register twice bigger of the cross sectional area, what would that be, of the duct or the silencer?
The answer to this question is above. RE: air velocity needs to be <300 FPM
Greg