rod gervais wrote:Luftweg,
I keep repeating to people the same mantra - but suppose I have to sit them down and make them breathe properly in order for them to get it.
I haven't gone through it yet with you - so I will now.
Repeat after me:
(while kneeling in the lotus position with your hands raised and the thumb with pointer finger forming an "O" - the remaining finger poined upwards).
Whatever I can make perfect I will make perfect - whatever I have to live with I will Live with....
That's too funny!
Anyway, I tore out all the old studs and insulation (will try to re-use what I might be able to)....
The book is great, and I see the issues with the fire-stopping that I need to take care of (actually pretty straightforward it seems). Thanx for enlightening me.
EXISTING DUCT WORK:
I have decided, if cost is not ridiculous, to use the JM Superduct stuff to replace the overhead sections of ducting that runs under the joists and between them.
I will call a place called 'Homans' in Wilmington, MA to see if I can get the stuff there....
There is a main duct (8" x 14"), 2 square ducts (5") that run right over the middle of the room location (b/t the joists), and 2 circular (5") ducts that run right over the concrete walls by the last joist (always forget the name of that one).
Since the concrete is 12 inches thick, most of the duct is over the concrete wall, and the penultimate joist sits just a couple inches from the inside plane of the concrete wall.
Should I just then block off this area somehow, instead of trying to get sheet-rock b/t the joists? (might still be able to get the sheet rock up, but would HAVE to pull the ducts out I think... then should replace them with the JM stuff? $).
I want to decrease the depth of the main duct, but widen it to compensate the loss in area -- IF that's recommended -- something like 6" by 18"....
What do you think?
ABOVE FLOOR AS SECOND LEAF:
Obviously , I have also decided that turning the above floor into the second-leaf IS the best idea -- as I've been told, and now see in your book.
Anyway, I'm about ready to add sheet-rock to the above floor, b/t the joists.
JOIST STRENGTH AND SPAN:
I have pretty much determined that the floor and joists can 'take' it....
The above room is a bedroom (thus 30 psf live) with 3/4" plank underlayment and red oak hardwood floor, AND wall-to-wall carpet over that.
The joists are:
2x8 hem-fir (probably 'northern'),
straight grain, few if even any knots, no termite/pest or water/mold/rot damage, and are 'old' lumber circa 1959.
They appear to be an easy grade 2.
Span is 12 feet even on the longest side, and about 8 feet on the other side.
In summary:
live 30 psf, dead 20 psf, L360 deflection, gives 12' 5" as a maximum span for grade 2, 2x8 hem-fir at 16 OC..... If it's only 15 psf dead, it would give 13' 1".
Northern hem-fir would give the 14' 2" to 14' 6" range.
** Now questions about page 64:
You show a similar floor, but with 2x10's, that says with hardwood flooring the dead load is 8 psf.
1.) Since the 2x8's are lighter, would that mean the dead load would also be a bit less? (probably not all that much, huh?)
2.) If so, would that allow for the carpeting weight, and do you think that I likely could add 2 layers of sheet-rock between the joists (as an added 5.7 psf?).
.... Oh yeah, I am considering the Green Glue also, since I'm only using 2 layers.....
STEEL JOISTS:
Might try to get 3 layers on the inner-leaf ceiling, and go with 4 x 1.65 inch, 20 gauge steel joists -- may use 2 of those or some other 'boxed' or 'back-to-back' steel joists for increased strength/safety, IF that's feasible.
The reason for using steel is the desire for a somewhat shorter depth in order to save precious ceiling height (walls will still likely use wooden 2x4 studs)
CROSS-BRACING:
Finally:
3) Can I safely remove ALL the crossbracing when I add the sheetrock, or do I have to do one section at a time, replacing the cross-bracing after each section is done?
I intend to get some pics and updated plan diagrams up as soon as I can....
thanx for your help,
K
P.S.
I haven't forgotten about the HVAC for the room....
Keep in mind that this is going to be a single room studio, and as such I will only require 1 inlet and 1 outlet.
Also, I will probably wanting to be using the adjacent understairs area as a 'buffer' room that will house fans and such....
The remaining basement is dehumidified and cool 365 days of the year (probably due to the concrete, the surrounding earth, etc), so I'm initially planning on just 'equalizing' ventilation with the rest of the basement -- through isolated ductwork (as per your book)....