Hi Stuart,
Thanks for the fast response, especially as you're short on time.
Right. Which is why you will probably need silencers on both sides, or a massive sleeve that goes through both leaves and is decoupled on both sides.
If I was to build a massive sleeve to go through both leaves please can you point me to some other posts about how to decouple this (having trouble finding an example)? I'm guessing it needs decoupling before it goes through either leaf but then I'm thinking I'm back to the issue I'd have with flexi duct where there's a 'thin' point in the cavity for sound waves to penetrate easily? Possibly I'm best to just go with a baffle box on the outside of the building.
I've since had a long read around the forum since I first wrote the above paragraph. I'm confused! I see you saying to someone that
I NEVER pass a duct directly through a leaf. That would be rather silly! The hole and the duct would totally trash your isolation. Instead, I design a wood "sleeve" that passes through the leaf. The wood sleeve has the correct internal cross section, and the duct connects to the end of it, on the other side of the leaf.
I'm confused as to why making a sleeve that passes from the back of the silencer to go through the inner leaf is much different than a well sealed plastic pipe if the silencer box is tightly mount to the inner leaf with no gap behind it? This was what I planned to do. I will change it if it's key to isolation to have a sleeve though?
The other bit I'm stuck on is the calculation for cross section of the silencer. The easiest thing for me is to use 100mm plastic pipe through my outer leaf connected to insulated flexi ducting which then connects to another bit of plastic 100mm pipe through my inner leaf directly into the back of my inner leaf mounted silencer box, all leaf penetrations will be sealed with acoustic caulk. Is 100mm pipe for inlet and outlet from the outer leaf sufficient for the size of the room? I have a 100mm core drill bit already bit can rent a bigger one if needed.
I understand that the silencer or point where the pipe enters the baffle box should at least double in diameter. Is this true of the reduction on the baffle box for the air output?
My flow rate is:
h=2.380m x w = 3.545 x L = 6.685 volume = 56.4 m3
Flow rate 56.4 x 6 = 338.4 cubic meters per hour
I see from other posts that
speed of air should not exceed 300fps
or 91.44 m/s (not sure this conversion to metric is right though as my results seem crazy!
A = q / v
where
A = duct cross sectional area (m2)
q = air flow rate (m3/s)
v = air speed (m/s)
which would mean A = q / v
where
A = duct cross sectional area (m2)
q = air flow rate (m3/s)
v = air speed (m/s)
a = 339/91.44 = 3.7m ??!
where did I go wrong? This is something I need to work out urgently so I can give the carpenter the right information. The silencer boxes will be built out of 22mm OSB with a layer of 15mm around the outside to achieve the same thickness as the inner wall.
If I do put a baffle box outside the building what's the best thing to clad these in? I've got plenty of OSB to make them out of but we've just a very nice looking extension done and you would see the inlet baffle box from the front of the house, by the front door

The wall is white rendered behind it so I'd want to make it blend in as much as possible.
Update
-------
So I'm having a few issues, I found this before - it's tricky getting trades to work at the level of detail required for a studio build. I've found various timbers touching the outer leaf

I'm getting those taken out and redone, it's frustrating. Is there a minimum gap I must have between any point on the 2 leafs? 'm referring to where the inner leaf rafters have diagonally cut ends in order to avoid contact with the outer leaf (lower section of roof rafters that are covered with 22mm chipboard and 10mm OSB)? This gap is small but it is a clear gap and my understanding that any break should work? Or am I wrong and vibration will travel across a gap if it's too small? I'm not that happy with this design choice but it was the best we could come up with to maintain the height of the room. See the photo for the gap I'm referring to:
joistsInplace.jpeg
I've also noticed that, despite me saying it was key to not leave a big gap at the bottom of the layers, on the inner leaf there are points where it's up to 10mm! I have some backer rod and will get this filled with acoustic caulk but isn't better to to have these floor to ceiling? The floor is a screed with insulation and 2 DPMs so there should be no moisture penetration.
innerleafbottom1.jpg
I've already got the door design sorted with 2 rubber trunking seals (chrylser type recommended in Rod's book), both doors are oak FD30 with 3/4 " plywood on the back. Both doors also to have strong fire door closers. I may add the magnetic strips if the isolation isn't good enough to the adjoining room but budget is tight so I'll try without first. One thing I've notice is where the carpenter has installed the outer leaf door lining there are the usual gaps between it and the masonry wall. This obviously must be filled with some material with mass. What do you recommend? The gap above the head is quite large. I could have this filled with a concrete mix and the caulk any small gaps/cracks? the sides are a little more tricky and are still too big for caulk. Here's a couple of photos:
outerdoorframe2.jpg
outerdoorframe1.jpg
Separate point
---------------
An interesting issue came up with the inner leaf ceiling joists today. When I saw how much the ends needed to be cut on a diagonal to avoid touching the outer leaf (technically my middle leaf that I have because of the tiled roof) rafters that are OSB boarded out for my middle leaf I was concerned about strength to take the weight of my inner leaf ceiling.
Here's a photo of the cut joists on sitting on the wallplate. If highlighted the diagonally cut ends in red. Before you panic, I had my structural engineer work out if they could take the sheer load of 1 layer 22mm OSB board + 1 layer 15mm soundbloc plasterboard and it's easily ok with this reduction in timber thickness at the wallplate. I was surprised and asked about 4 times, until he was almost annoyed!
Here is the sketch we did for him and a photo of a cut 8x2 rafter held over a piece of CLS (same as used for the wallplate). One diagram shows a single wallplate and the other shows a double. He said either worked but the double plate was a better option so we've gone with that, even though it means the joists got cut thinner to get the diagonal.
joistendsketch.jpeg
here's the photo:
actualjoistendmeasurement.jpeg
I thought this was interesting as there's a lot of talk about how heavy these ceilings are, and they are! But I found it interesting that 8x2 rafters at 400mm centres can take this load so easily that cutting the bearing ends down like this is still ok. The structural engineer is highly respected in my area of the UK so I'm sure he's correct.
The other thing to factor in, that the structural engineer left out of his calculations but said would help some, is the walls are clad in 22mm OSB which butts right up under the joists providing more support for them as it kind of extends the wall plate inwards.
Thought I'd share that last bit as a point of interest.
This question is a bit late in the day as we've already started build the studwalls with a vapour barrier but I have been reading some conflicting opinions on vapour barriers. They seem like a good idea in the winter when the room is warm and it's cold outside. Check the vapour on the warmside of the insulation to provent interstitial condensation in the insulation or cavity. But when it's hot outside (not that hot in the English summer!) and cold in the room thanks to the AC then surely the reverse is true potentially leading to condesation on the outside of the vapour barrier leading to damp/wet timbers and insulation in the cavity and roof space? Maybe the AC and air inlet/outlet with fan is enough to control the vapour levels in the room but nothing is controlling them behind the studwalls in the Summer. Because I sealed my concrete bricks on the outer leaf they won't allow much if any vapour to evapourate which means it can only evapourate upwards towards the roof space. It would have to go through my middle leaf of 22mm chipboard + 10mm OSB first though. Maybe I'm overthinking this but I've seen how much water can appear from condesation in the roof of my house when we first bought it and it had no insulation, the rafters were literally dripping until we had the issue sorted and put some ventilation up there as well as insulation. Appreciate your thoughts on this, please keep in mind I live in the UK so that's the climate we're dealing with.
Thanks
Ricky