Great, thanks!!Gregwor wrote:Sounds about right!
Greg
Groundlift Research & Development NEW STUDIO (consolidated)
-
- Posts: 58
- Joined: Sun Apr 22, 2018 6:28 am
- Location: Los Angeles, Ca. USA
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
S. Husky Hoskulds
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
-
- Posts: 58
- Joined: Sun Apr 22, 2018 6:28 am
- Location: Los Angeles, Ca. USA
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
ps - any thoughts on those numbers re: the HVAC?
(a couple of posts up)
(a couple of posts up)
S. Husky Hoskulds
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
-
- Posts: 36
- Joined: Thu May 25, 2017 8:09 am
- Location: Arcata, California USA
Re: Groundlift Research & Development NEW STUDIO (consolidat
Been following this thread. I am also working on my HVAC plan. Did you ever get a response regarding your calculations for duct size?Darth Fader wrote:ps - any thoughts on those numbers re: the HVAC?
(a couple of posts up)
-
- Posts: 58
- Joined: Sun Apr 22, 2018 6:28 am
- Location: Los Angeles, Ca. USA
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
Hi there, Howiedrum.
not yet, but I'll let you know if anything develops!Been following this thread. I am also working on my HVAC plan. Did you ever get a response regarding your calculations for duct size?
S. Husky Hoskulds
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
-
- Posts: 36
- Joined: Thu May 25, 2017 8:09 am
- Location: Arcata, California USA
Re: Groundlift Research & Development NEW STUDIO (consolidat
Thank you. I met with the HVAC local guy that my contractor recommended and he was clueless. To his credit he didn't try to sell me on anything and said he would bid the job as I wanted to do it but he wasn't much help. He had never heard of NC ratings. Gasp! So I am back to the drawing board.not yet, but I'll let you know if anything develops!
-
- Moderator
- Posts: 1501
- Joined: Wed Feb 01, 2017 6:03 pm
- Location: St. Albert, Alberta, Canada
Re: Groundlift Research & Development NEW STUDIO (consolidat
Your 690 CFM checks out with me.doing some math on the HVAC system, wondering if you guys could have a quick look over my numbers, to see if I'm on the right track?
(this is for the proposed control room)
Size: 20x30x11.5
Volume: 6900 cubic ft
x6 changes per hr: 41400 cubic ft
divide by 60 mins: 690 (cfm?)
according to my online duct calculator, given the target would be 300 fpm at registers, the ductwork inside the control room would need to be somewhere close to 20.5 in diameter, for a round duct, and 10x30 for rectangular ducts.
this sounds pretty substantial for a 20x30 room.
is this correct?
(not sure i've ever even seen a 20" round duct, in person )
or... would this be split before entering the control room?
and that then bringing the total number of silencers to 8, for a single room??
ps (edit) - actually, just got out my measuring tape and looked around the room a bit... 20" in diameter, for a single duct, doesn't actually look crazy.. it just sounds kinda outrageous on paper.. so maybe a single 20" supply wouldn't be quite as Hindenburg looking as i was afraid it would be
or, maybe a single 10x30 duct down the middle - or halfway - would look pretty ok as well.
Here's your duct sizing (see bottom of pic) These are all common residential duct sizes. But, your silencer boxes will be HUGE. You might be better off having two supply lines at half that CFM - Closest leaning to larger would be 400CFM.
For air velocity of 300 ft/min, I calculate:
690CMF / 300ft per min = 2.3 square feet
2.3 square feet x 144 = 331 square inches. That's huge. That works out to about an 18 1/4" x 18 1/4" interior dimension for your silencer boxes.
So, again, splitting that in 2 or even 4 would be awesome. It seems like your math is good. And yes, every duct would need a silencer on it. So, 1 supply and return would be your typical 4 silencer build. 2 supplies and returns = 8 silencers. 3 = 12 silencers, 4 = 16 silencers.
Personally, since my builder screwed me over in at least one of my rooms, I have a small room (200CFM) where I'm going to have to build 3 supply lines (6 silencers) so that I can get the air velocity slow enough through my ceiling joists (luckily they used 14" deep I-Joists). Brutal, but do it right or don't do it at all.
Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
-
- Site Admin
- Posts: 11938
- Joined: Thu Aug 21, 2008 10:17 am
- Location: Santiago, Chile
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
There seems to be some big confusion here: You do NOT need such low flow velocities inside the silencers: the oft-quoted 300 fpm figure is for the air velocity at the REGISTERS, not inside the duct-work. The velocity can be much greater inside the ducts and silencers, as long as there's a decently long section where it has already been slowed down just prior to the register. And especially on the part outside the outer leaf: the velocity out there really doesn't matter at all, as far as the studio is concerned (although it might matter for the neighbors...)For air velocity of 300 ft/min, I calculate:
690CMF / 300ft per min = 2.3 square feet
2.3 square feet x 144 = 331 square inches. That's huge. That works out to about an 18 1/4" x 18 1/4" interior dimension for your silencer boxes.
- Stuart -
-
- Posts: 58
- Joined: Sun Apr 22, 2018 6:28 am
- Location: Los Angeles, Ca. USA
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
Howiehowiedrum wrote:Thank you. I met with the HVAC local guy that my contractor recommended and he was clueless. To his credit he didn't try to sell me on anything and said he would bid the job as I wanted to do it but he wasn't much help. He had never heard of NC ratings. Gasp! So I am back to the drawing board.not yet, but I'll let you know if anything develops!
As Stuart pointed out, earlier in this thread, most HVAC guys will not know the first thing about studio HVAC design.
The key to your (our) success would be - as he said - to do the calculations ourselves (it's not very complicated once you sit down and make a list of all the cfm's, mph, fpm's, cuf's, abc's and lmnop's) and then have the builders install / build to your (our) specs, right Stuart?
Once i sat down and wrote a few things down on paper, and plugged in the numbers, it's not crazy complicated - i think.
I reckon the hardest part (which may actually have lucked out with) is finding a guy or gal that actually gives a damn enough to listen to you and then really do what is asked.
Keep us posted!!!
S. Husky Hoskulds
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
-
- Posts: 58
- Joined: Sun Apr 22, 2018 6:28 am
- Location: Los Angeles, Ca. USA
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
This is good stuff, Stuart!There seems to be some big confusion here: You do NOT need such low flow velocities inside the silencers: the oft-quoted 300 fpm figure is for the air velocity at the REGISTERS, not inside the duct-work.
Thanks for chiming in.
So, that begs the question: with 4 (for example) registers in a control room, roughly 20x30, would it make sense to have the same size ductwork (or close to it) feeding four legs of supply? And thus acheive enough of a 'slow down' that way?
In other words: if i feed the room with a single 18" supply (hypothetically) and split it off to 2 or 4 registers (like an ... ehm .. octupus with 4 legs, y'know) and kept each leg the same diameter, that would be smart?
The typical design, residentially and commercially, it seems (logically) would the the "big supply getting smaller and smaller" type deal, as airspeed is not an issue.
Thoughs?
Am i close?
S. Husky Hoskulds
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
-
- Site Admin
- Posts: 11938
- Joined: Thu Aug 21, 2008 10:17 am
- Location: Santiago, Chile
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
Think of it this way: there is a direct, unbreakable relationship between the air flow velocity, the air flow rate, and the duct cross section. Since the AHU fan will be moving air at a fixed RATE and VELOCITY as it comes out of the unit, you can control the VELOCITY in the rest of the system ONLY by varying the cross sectional area of the duct. If you increase the cross-sectional area, then the VELOCITY goes down, but the RATE stays the same. If you decrease the cross sectional area, then the velocity goes up, but the rate stays the same. However, decreasing the cross-sectional area also decreases the AIR PRESSURE (Bournelli's theorum), but increases the STATIC pressure, and considering that your AHU will have certain limits on how much pressure it can handle, you do have to be careful (just making the duct longer also increases the pressure, even if there is no change in cross-sectional area).So, that begs the question: with 4 (for example) registers in a control room, roughly 20x30, would it make sense to have the same size ductwork (or close to it) feeding four legs of supply? And thus acheive enough of a 'slow down' that way?
Think of it like water flowing through your garden hose pipe: It is moving at a constant rate. If you put your thumb part way across the end of the hose, then that changes the pressure and velocity, but not the rate. To increase the rate, you have to turn the tap on harder.
So there's this relationship between velocity, rate, pressure, and cross-sectional area. To be more precise, the TOTAL energy in the moving air is the sum of the KINETIC energy and the POTENTIAL, and it is fixed: you cannot increase or decrease the total energy of the moving air, except by adjusting the AHU controls. If the kinetic energy goes up at some point in the the system, then the potential energy MUST go down, such that the total stays the same. And vice-versa: if the potential energy goes up, then the kinetic energy goes down by the same amount. If this were not true, then airplanes and birds would not be able to fly.
Therefore, changing the cross-sectional area at various points throughout the system is the ONLY parameter that you have control over in the design. Since you can easily check the manufacture's specifications for the AHU to find out what air flow rates and air flow velocity it produces at various settings, you can easily determine what the total cross sectional area is that you will need at your register, in order to ensure that the velocity NEVER goes over 300 FPM, even when the AHU is running at the highest setting.
So that's your starting point: You will do the math, and figure out that you need "X" square inches of cross sectional area at your register.
Now go to your local HVAC supply store, and look at registers: If the ones you are looking at that have the correct area just seem to be too big for your room, then you will probably have to split the air-stream at some point and use two smaller registers, that STILL ADD UP TO THE THE SAME TOTAL AREA. And if those smaller ones still seem too big, then you will need to split the airflow again, into FOUR registers, once again where the individual areas of those sum to the correct total area.
There's another factor to take into account here: "open area". Registers have frames around them, and vanes on them that direct the air flow into the room. Those block some of the total surface area. So for example a 10" x 10" register would seem to have 100 square inches of area, but by the time you allow for the frame and vanes, there might only be an actual cross-sectional area of maybe 70 square inches. IF the vanes are adjustable, the more you angle them, the less area is left. So take a very close look at the specs for the register, to determine how much REAL area is left over. And also look at the "smoothness" of the design: registers that have lots of protrusions and sudden sharp edges will create turbulent air flow which is noisy. With better designs, the vanes are smooth and "aerodynamic", which creates a lot less turbulence.
OK, so now you have your registers figured out: that automatically defines the duct that leads to the register! You have no options here. If the duct is 8" x 6", then the duct has to be AT LEAST 10" by 8", because it is going to be lined with 1" of duct liner on the inside, all around. Or if you are using round duct, then it needs to have the same "equivalent cross-sectional area" as the rectangle of the register.
So now you know the correct size of your registers, and the correct size of the ducts that lead to the registers, and you know that you need a long straight section of duct right before the register, to reduce turbulence. But how long does that straight part have to be? There are various methods for calculating that, but a good rule of thumb is that it should be at least three times the smallest dimension of the duct. So if you are using an 8" x 6" duct, then you need at least 3x6"=18" of straight duct before the register. That's the ideal, of course, but frequently that just isn't possible in a studio. So you do your best to make it as long as possible, and aim for an even lower velocity at the register, to reduce the noise from turbulence even more.
So, at this point you have your register size, duct size, and final duct length. Now you go another step back up the chain: the silencer box. Once again, there's a general rule here, that the cross-sectional area must change suddenly by a factor of at least two, where the air enters the box and where it exists the box. So normally the area inside the box is twice the area of the duct. In other words, if you figured that your duct needs to b 8x6, that works out to 48 square inches, thus you need 96 in2 cross sectional area (minimum) inside your silencer. So you could make it 11" x 9" which is 99 in2m or you could make the box flatter, for example 12" x 8", which is 96, or even 16" x 6" (also =96). OF course, in theory you could make it ultra-flat, at 96" x 1", but in reality that won't work, as the static pressure would be too high from such a system. So keep your dimensions reasonable, and never go below about 6" on the smaller dimension.
However, once again, this is the cross-sectional area that the AIR FLOW sees, not the actual internal dimensions of the wood. Why would that be different? Because the box is lined with duct liner! Just like your rectangular duct there's 1" of true HVAC duct liner on each side. So if your calculations show that you need 12" x 8" internal cross section, then the interior of the wood box needs to be 14" by 10" at all points. Add the thickness of the wood, and you get the actual EXTERNAL dimensions of the box, at that point. Assuming that you are using 1 1/2" thick wood, you'd add 3", to get a final external size of 17" x 13".
But that's just the width and height: how LONG does the box need to be? Well, you need a certain number of "baffles" inside the box: the more isolation you need, the higher the number of baffles. At the VERY least, you need two baffles. Probably three or four (usually). Maybe as many as five or six, for very high isolation needs. Each baffle is probably 1" thick plus 1" of duct liner on each side, so 3" thick. Plus the spacing between them (to get the same cross sectional area as above). So let's say you need three baffles spaced 12" apart, that works out as follows: (4x12) + (3x3) = 57" internal length, plus 3" wood = 60" total length. So for this hypothetical case, your silencer box would be 60" long, 17" wide, and 13" high.
Did I mention that silencers are usually pretty large?
So now we go yet ANOTHER step back up the chain: the duct on the far side of the silencer. How big should that be? Answer: it doesn't matter! As long as it is half the cross sectional area of the silencer interior, that's fine. If it is 1/4 the area of the silencer interior, that's also fine, EVEN THOUGH THE AIR FLOW SPEED WOULD BE MUCH HIGHER. It does not matter, because you'll never hear it! That can flow fast, or slow: it won't affect the noise level inside the studio, because it is on the FAR side of the silencer.
Of course, there are limits: the smaller you make it, the higher the static pressure, and you cannot exceed the total static pressure that your AHU can handle. So you have to be careful when adding up all the ducts, silencers, registers, dampers, and other things, to make sure the total static pressure from all of those is less than the capacity of the AHU. If the static pressure is too high, the AH will not be able to run efficiently, the fan blades will stall, the motor will overspend, the service life will be very much shorter, and you won't get the performance you were planning on, either in terms of ventilation or in terms of cooling.
And so on. You keep on working backwards up the chain, doing the math for each part, to make sure that you have the flow rates, flow velocities, and static pressure within the range that you need.
"Range that you need"? What's that? Well, to dimension the actual AHU itself, you must ensure that it is able to move enough air to replace all of the air inside your room, at least 6 times per hour. In other words, if the volume of your room is 2000 cubic feet, then your AHU must be able to move at least 12000 cubic feet per hour, and if you divide by 60 then you get cubic feet per minute: 12000/60 = 200 CFM. For that room, your HVAC AHU would have to be capable of moving 200 cubic feet per minute (air flow rate) at a velocity that will produce no more than 300 FPM AT THE REGISTERS, on the highest setting. That's just the specs for how it moves air: in addition, you need to calculate the spec of how much heat it must be able to add/remove, and that, in turn, depends on the sensible heat load and the latent heat load. But that's an entirely different subject...
That probably didn't answer your question directly, but there's enough info in there for you to be able to figure it out, I hope...
-
- Moderator
- Posts: 1501
- Joined: Wed Feb 01, 2017 6:03 pm
- Location: St. Albert, Alberta, Canada
Re: Groundlift Research & Development NEW STUDIO (consolidat
Assuming the register cover is directly on the outlet of your silencer box, there wouldn't be enough duct work (3 times the smallest dimension) to deal with turbulence.There seems to be some big confusion here: You do NOT need such low flow velocities inside the silencers: the oft-quoted 300 fpm figure is for the air velocity at the REGISTERS, not inside the duct-work. The velocity can be much greater inside the ducts and silencers, as long as there's a decently long section where it has already been slowed down just prior to the register. And especially on the part outside the outer leaf: the velocity out there really doesn't matter at all, as far as the studio is concerned (although it might matter for the neighbors...)
I've found that twice the cross sectional area of your inlet size often ends up being close to the <300 ft/min air velocity anyway.
Thanks for sharing this info though as it will probably help me out with my lack of space in my ISO room!
Greg
It appears that you've made the mistake most people do. You started building without consulting this forum.
-
- Posts: 58
- Joined: Sun Apr 22, 2018 6:28 am
- Location: Los Angeles, Ca. USA
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
Stunning, Stuart!!That probably didn't answer your question directly, but there's enough info in there for you to be able to figure it out, I hope...
Thank you - yet again - for all this info!
i feel armed, and ready!!
Onward!!!!
S. Husky Hoskulds
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
-
- Site Admin
- Posts: 11938
- Joined: Thu Aug 21, 2008 10:17 am
- Location: Santiago, Chile
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
Ahh, but we are just getting started! Barely scratching the surface, so far ...i feel armed, and ready!!
- Stuart -
-
- Posts: 58
- Joined: Sun Apr 22, 2018 6:28 am
- Location: Los Angeles, Ca. USA
- Contact:
Re: Groundlift Research & Development NEW STUDIO (consolidat
Gotta start somewhere!Ahh, but we are just getting started! Barely scratching the surface, so far ...
S. Husky Hoskulds
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
Recording Engineer
Los Angeles, Ca.
U.S.A.
https://en.wikipedia.org/wiki/S._Husky_Hoskulds
https://www.instagram.com/le_darth_fader/
-
- Posts: 36
- Joined: Thu May 25, 2017 8:09 am
- Location: Arcata, California USA
Re: Groundlift Research & Development NEW STUDIO (consolidat
Thank you all. I got up at 5:30am because I was thinking about HVAC. It is such a roller coaster. After Greg's post I was "yeah" then after Stuart's I was "oh". Very helpful!
Howie
Howie